My textbook says:
watts loss = load * load / resistance
although i can easily enough plug in numbers, i wonder what it all means.
if watts loss = 100
does that mean power consumption = load + watts loss?
|
|
|
|
Joined: Mar 2002
Posts: 582
Member
|
I'm not sure what result your looking for. Checkout this website for some power (wattage) formula http://www.tpub.com/neets/book1/chapter3/1-7.htm [This message has been edited by Ron (edited 02-09-2005).]
Ron
|
|
|
|
Joined: Nov 2004
Posts: 138
OP
Member
|
thanks, i'll check it out. i'm just trying to figure out what exactly watts loss is. my boss looked at me like i was crazy when i told him about it.
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
watts loss = amps x amps x resistance of the conductor in your example. This is the energy that heats the conductor. The amps used is the load amps.I often see ads that show cost saving benefits by increasing wire size above what is normally required by the NEC. Depending on the load and length of time the plant is in operation, it can be shown that the added wire size can return the extra costs over a short period of time.
[This message has been edited by Bob (edited 02-10-2005).]
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 4
Member
|
Good call Bob!. Yes, any loss within an Electrical system can be put down to I2R, provided that it is a resistive load. And it is usually a Heating effect. However, should the load involve things like Capacitive and Inductive Reactance, things become a tad more difficult, with respect to the total impedance offered to the Supply Voltage.
|
|
|
|
Joined: Nov 2004
Posts: 138
OP
Member
|
thanks, Bob. so the eccentric homeowner how we just ran 12 wire for everything in his home (except the range, dryer, ect) was actually on to something.
|
|
|
|
Joined: Oct 2003
Posts: 156
Member
|
clydesdale, it might help you if you were to draw out a simple circuit and do the math using ohms law to see how it works. Just use a source like 120 VDC, load resistor of 144 ohms (equivalent to 100 W light bulb), and say something like 2-2 ohm resistors representing each leg of the wire and see what you come up with.
I will give you a hint to one of the numbers you should come up with 96.6
|
|
|
|
Joined: Oct 2003
Posts: 156
Member
|
Bob, I have to disagree with your statement with respect to resistive loads. If you were to use a larger wire with less resistance on a resistive load, you would increase the load current, thereby cost more to operate, not save.
|
|
|
|
Joined: May 2004
Posts: 186
Member
|
My $ is with Bob on this one. I dont quite figure how using a smaller cable will reduce I2R loss on any given load.
|
|
|
|
Joined: Feb 2002
Posts: 182
Member
|
Clydesdale "thanks, Bob. so the eccentric homeowner how we just ran 12 wire for everything in his home (except the range, dryer, ect) was actually on to something." In a residence it would take forever to get a reasonable return on the investment because the load is not on that long. dereckbc For a resistive load that is online for a long time I think you would be correct. My point was "Depending on the load and length of time the plant is in operation, it can be shown that the added wire size can return the extra costs over a short period of time." This idea is for large loads that run all day and night.
|
|
|
Posts: 34
Joined: June 2004
|
|
|
|