We have a bathroom with the tile floor heating comming up. We done them before but was wondering somthing. If the tile guys leave way to much heating wire in your box can it be cut to fit? Or does that case problems with the resistancee? Can it be put in the box or will the box get too hot. Do we just need to make sure the tilers use up the extra wire in the floor and not the box?

If I remember on 1 mat there are 2 leads with a metal sheald. The shield would be grounded?

Tom

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

#48216 02/06/05 02:07 PM
Joined: Apr 2002
Posts: 558
C
Member
The heating leads should never leave the floor. The non-heating leads can be cut as desired and yes the shield should be connected to the EGC.

Curt


Curt Swartz
#48217 02/06/05 05:39 PM
Joined: Feb 2003
Posts: 687
A
Member
OK. So the leads going to the controler don't heat up.