#48078 02/03/05 10:49 AM
Joined: May 2003
Posts: 74
J
jkraft Offline OP
Member
My local road commision has purchased a 90KW generator with a 400A automatic transfer switch, suitable for use as service equipment, and wants me to connect it. The building is one of their maintenance garages and has a 2000A service with a 800A main. The supervisor wants me to down size the fuses to 400A saying that's all the service they need. I haven't done an actual load survey yet, but am concerned if the local inspector will even allow this. Any ideas?

#48079 02/03/05 12:10 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
Do the load calc's and see what you come up with.


Ryan Jackson,
Salt Lake City
#48080 02/03/05 02:49 PM
Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
Why not put a 400 amp fused panel at the generator or on the building and leave things as they are?
Also check with the utility and get the yearly max demand.
What is the voltage?



[This message has been edited by Bob (edited 02-03-2005).]


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Radar
Radar
Los Angeles
Posts: 349
Joined: April 2004
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,563 Are you busy
231,912 Re: Forum
216,547 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5