3- 15kw heating units #4801 10/18/01 12:02 PM
Joined: Oct 2001
Posts: 1
A
andy19 Offline OP
Junior Member
I HAVE A 200 AMP 120/240V 1PHASE M/L/O LOAD CENTER PANEL IN A MODULAR SCHOOL BUILDING
THAT THE MANUFACTURER INSTALLED 3 -15KW 240V
1 PHASE IN. TOTAL LOAD OF 198 AMPS WITH BLOWER MOTORS. I'M PLANNING ON FEEDING THIS SUB PANEL WITH A 200 AMP FUSE DISCONNECT. anything IN THE NEC THAT SAYS I CAN'T DO THIS? I'VE ASKED SERVERAL PEOPLE AND THEY SAID I COULDN'T BUT COULDN'T GIVE ME A CODE REFERENCE.
THANKS FOR YOUR HELP
ANDY

[This message has been edited by andy19 (edited 10-18-2001).]

Work Gear for Electricians and the Trades
Re: 3- 15kw heating units #4802 10/19/01 08:40 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Andy,

The best I can say is "maybe."

See 220-15, the exception seems to offer some wiggle room. If all units will be on at the same time, what about the lights & receptacle load, are they on another feeder? Seems to me that there is not enough capacity. To apply the exception, you'll need permission from the AHJ.

Tom


Few things are harder to put up with than the annoyance of a good example.
Re: 3- 15kw heating units #4803 10/20/01 03:08 PM
Joined: Aug 2001
Posts: 142
B
bordew Offline
Member
Andy:
Wouldnt this be considered a continuous load?
210.20(A). So if your load is 198 amps with that kind of load the conductors could also be used as heaters (?)
Just by that the rating should be 247 amps or 125% of the load + the non-continuous load. Also art. 424.3(B) Branch circuits, fixed electric space heating equipment, shall be rated at 125 % of total load and motors.
I would think you need a bigger panel.

Re: 3- 15kw heating units #4804 10/20/01 09:10 PM
Joined: Dec 2000
Posts: 4,283
electure Offline
Member
I think I'd contact whoever it was that supplied this piece of "art", and have them give you something that is Code compliant.
If it's going in a school, the school district should at least have enough clout to get something safe from them.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,787 Are you busy
205,000 Re: Forum
193,115 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3