Buck Booster #47440
01/17/05 08:31 AM
01/17/05 08:31 AM
D
Dave55  Offline OP
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I'm installing a 0.5 KVA transformer for a tanning bed. The house voltage is 251V 1PH and I need to bring it down in the 215-230 range. The manufacturer of the tanning bed is shipping the transformer with the bed. I haven't installed one this small before, and am curious about it's size.

Is this going to require a separate cabinet, or will it fit in the distribution panel? Will it require some type of ventilation?

Dave

Work Gear for Electricians and the Trades
Re: Buck Booster #47441
01/17/05 08:40 AM
01/17/05 08:40 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Dave any buck boosts I have installed have looked like this

[Linked Image]

This one happens to be .5 KVA so the size will be approximately the same as yours.

6" x 6" x 5" don't count on those measurements but it will be somewhat close.

I usually put these right at the panel.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Buck Booster #47442
01/17/05 10:43 AM
01/17/05 10:43 AM
C
circuit man  Offline
Member
Joined: Nov 2001
Posts: 273
saluda,s.c.
dave, why is the house voltage so hi?it should be around 240 or a couple above.i bet electronics don't last long.have they contacted the power company about this?

Re: Buck Booster #47443
01/17/05 10:44 AM
01/17/05 10:44 AM
C
circuit man  Offline
Member
Joined: Nov 2001
Posts: 273
saluda,s.c.
is this a single phase service? not from a three phase bank.

[This message has been edited by circuit man (edited 01-17-2005).]

Re: Buck Booster #47444
01/17/05 10:51 AM
01/17/05 10:51 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Circuitman 251 volts is a little under 5% high, it is not that bad.

You could talk to the power company I doubt they would do anything.

UL requires equipment to handle + or - 10%


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Buck Booster #47445
01/17/05 11:22 AM
01/17/05 11:22 AM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
To go on a little I will show some info from "Voltage Ratings for Electrical Power Systems and Equipment, American National Standard ANSI C84.1–1989"

The power company does not have to follow this but they may.

For a 120/240 3 wire service the voltage at the service should be between 91.7% (220 volts) and 105.8% (254 volts)

The voltage at the utilization equipment should be between 88% (212 volts) and 105.8% (254 volts)

You can get more info with an Internet search for ANSI C84.1–1989

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Buck Booster #47446
01/17/05 11:27 AM
01/17/05 11:27 AM
D
Dave55  Offline OP
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
I don't know much about POCO stuff, but I'd say it's intentionally set at the high end so a voltage drop will keep it in range.

Dave


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
MarkC10
MarkC10
CA, Inland Empire
Posts: 43