400 amp service #47417
01/16/05 05:36 PM
01/16/05 05:36 PM
E
eswets  Offline OP
Member
Joined: Mar 2004
Posts: 55
Lansing, IL, USA
The state I used to work it, it was common pratice for a 400amp residential service to really be a 320amp. The meter was a 320amp rated meter socket that feed 2 200amp (main breaker) panels with 2" pipes and 3/0's to each panel. I have changed to a different region, and am wondering if this is standared everywhere or if this is not the right way to do this.

Work Gear for Electricians and the Trades
Re: 400 amp service #47418
01/16/05 05:43 PM
01/16/05 05:43 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
It is fine, a 320 meter is rated 320 amps continuous, 400 amps non-continuous.

If a 400 amp service is properly sized it will not exceed 320 amps continuously.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 400 amp service #47419
01/16/05 07:23 PM
01/16/05 07:23 PM
W
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
Common practice in Mass. 320 amp continuous for a 400 amp service. 80%. I believe you have to be the full 400 amp on commercial services. Most of the electricians around here install it exactly how you explained except they use 4/0-3 SEU/AL. No pipe. Your way is much better, I guess around where I am they go the bare minimum requirements.

Re: 400 amp service #47420
01/16/05 08:43 PM
01/16/05 08:43 PM
T
ToHo  Offline
Member
Joined: Dec 2004
Posts: 46
N.Y.
wirenutt.. what do you guys in Mass. run for 400amp UG services?? what would be a typical meter and panel configuration be. Thanks..ToHo

Re: 400 amp service #47421
01/16/05 08:55 PM
01/16/05 08:55 PM
I
iwire  Offline
Moderator
Joined: Jan 2003
Posts: 4,391
North Attleboro, MA USA
Quote
I believe you have to be the full 400 amp on commercial services.


The only reason I can see that requirement is if you used 100% rated breakers and equipment.

A typical 400 amp breaker is only UL listed for 320 amps continuous or 400 amp non-continuous.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 400 amp service #47422
01/16/05 09:28 PM
01/16/05 09:28 PM
A
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
Thats how the 400 amp resedential are set up around here in IL. We don't call it a (2) 200 or 320 amp. Maybe more of a sales thing. Don't want to be pricing out a 320 amp when the other EC has the same set up calls it a 400 amp.

Tom

Re: 400 amp service #47423
01/16/05 10:12 PM
01/16/05 10:12 PM
E
eswets  Offline OP
Member
Joined: Mar 2004
Posts: 55
Lansing, IL, USA
Tom,
Im in IL I think around your area. Suburbs of Chicago. So using a 320amp meter socket with 2/200amp panels is ok for the 400 amp service?

Re: 400 amp service #47424
01/17/05 07:11 PM
01/17/05 07:11 PM
A
Active 1  Offline
Member
Joined: Feb 2003
Posts: 687
Grayslake IL, USA
Yep.

At the supply we just ask for a 400 amp pedistal but they know we mean 320 amp. Milbanks catolog for Com Ed only shows single phase 320 not 400 amp meter housings. Com Ed resi feeds underground are normaly 200 and 320 a. Overhead 100, 200, and 320 a.

We would only bond one panel and would run a larger water pipe ground than a single 200 a service, I think 1ott. You could do it other ways.

Tom

Re: 400 amp service #47425
01/17/05 08:28 PM
01/17/05 08:28 PM
W
Wirenuttt  Offline
Member
Joined: Nov 2002
Posts: 267
Massachusetts
TOHO; Mostly the Milbank # 2448-X meter socket. One EC uses 500 kcmil xhhw. Murray also makes a unique 400 amp double main break panel that's kind of interesting. Guess it depends on your situation.

Re: 400 amp service #47426
01/18/05 12:37 AM
01/18/05 12:37 AM
P
PCBelarge  Offline
Member
Joined: Jun 2003
Posts: 681
Dobbs Ferry, NY, USA
Tom
What do you mean by, "bond only one panel"?

Pierre


Pierre Belarge
Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HCE727
HCE727
Delaware County, PA, USA
Posts: 186
Joined: November 2005
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,521 Are you busy
190,760 Re: Forum
180,480 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.026s Queries: 15 (0.004s) Memory: 1.0226 MB (Peak: 1.1990 MB) Zlib enabled. Server Time: 2019-04-22 00:23:38 UTC