Sump pump outside #47209 01/11/05 09:39 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline OP
Member
I have a customer that is moving his sump pump outside. It currently is in a crawlspace under his master bedroom, and he is tired of hearing it cycle on & off at night, so they are digging a hole just outside, running the drain tiles to it, and then piping it to the storm sewer.

I want to avoid GFI to avoid nusiance tripping flooding the lower level. Any suggestions? I'm thinking an in-use cover with a single receptacle wouldn't fly because that exception only applies to the garage and basement.

Any suggestions?


Can I clip the cord and run it into an AC disconnect?

Work Gear for Electricians and the Trades
Re: Sump pump outside #47210 01/12/05 09:57 AM
Joined: Apr 2004
Posts: 349
Radar Offline
Member
Can't you find an applicable exception to the GFI requirement based on: a) receptacle location not readily accessable, or: b) single receptacle (not duplex) dedicated to equipment fixed in place (Art 210-8)?


There are 10 types of people. Those who know binary, and those who don't.
Re: Sump pump outside #47211 01/12/05 11:23 AM
Joined: Dec 2004
Posts: 52
K
kd Offline
Member
Hey, install a GFCI; it is required to protect people from shock. Perhaps install it on a wall indoors so it will not get moisture in it and feed the sump pump downstream. If it trips, try to find a 15 mili-amp tripping model. If that trips, you will have to replace the GFCI with a switch. At least you tried. I am assuming that it is a new sump pump or they cannot afford to get a new one.

Re: Sump pump outside #47212 01/12/05 12:54 PM
Joined: May 2004
Posts: 697
D
Dave55 Offline
Member
I'd keep the power cord and install a single receptacle with a WWIU cover. GFCI protection isn't required or recommended.

Dave

Re: Sump pump outside #47213 01/12/05 01:14 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
There is no code exception for this appication. The only excecption to 210.8(A)(3) is for snow melting equipment. You have 3 choices, 1) install the GFCI, 2) install a hardwired pump, or 3) install a 240 volt cord connected pump.
Don


Don(resqcapt19)
Re: Sump pump outside #47214 01/12/05 08:36 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline OP
Member
Thanks guys.

Don, I was thinking along the same lines as you, except I didn't think of your option 3.

I'll put this question to my AHJ, but do any of you see a problem with cutting off the end of the cord? I guess besides maybe that a plumber will be fiddling around with it when it comes time to replace it.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Mont Belvieu, TX
Posts: 437
Joined: December 2001
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,050 Are you busy
205,944 Re: Forum
193,996 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3