ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Upside Down ThreeWay
by gfretwell - 08/12/22 12:30 AM
Load Calcs for EVs and RVs
by gfretwell - 08/12/22 12:24 AM
Wiring method choice
by HotLine1 - 08/10/22 03:39 PM
NEC- 314.23 (H) (1)
by renosteinke - 08/10/22 11:13 AM
RV Forums
by gfretwell - 08/07/22 07:01 PM
New in the Gallery:
240/208 to a house
240/208 to a house
by wa2ise, October 9
Now you know.
Now you know.
by Tom_Horne, September 7
Who's Online Now
0 members (), 22 guests, and 23 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Aug 2004
Posts: 69
N
nov Offline OP
Member
I have a 200 amp main breaker panel and I am installing a 200 amp auto transfer switch. The SEU cable comes out of the panel and feeds into the transfer switch first the to the main panel. My question is if the transfer switch is hit first does that make the main panel a sub panel. Basically should I treat the transfer switch the same as a service disconnect. If it is a sub I would have to seperate the grounds and the neutrals and feed the main panel with SER cable.

Joined: Jan 2003
Posts: 4,391
I
Moderator
Yes the ATS will now be the main and the neutrals and grounds at the old panel will need to be isolated.

Question for you, is this a "Service Rated" transfer switch?

It must be in order to install it as you describe.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Aug 2004
Posts: 69
N
nov Offline OP
Member
I believe it is service rated it is a generac 200 amp transfer switch model 06435
http://www.guardiangenerators.com/support/guardian_transfer_switch.asp

Joined: Jan 2003
Posts: 4,391
I
Moderator
I am not sure that what you linked to is service rated.

I would expect to see accessible disconnect switches to kill the power, it looks like you need a screw driver to open them.

The page mentions UL 1008 Listed which is just a transfer switch listing not necessarily a "Service Rated" transfer switch.

Before purchasing this switch you want to be sure.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: Apr 2002
Posts: 558
C
Member
I don’t believe the transfer switch you are proposing to use is rated for use as service entrance equipment. It does not have provisions for a bonding jumper and doesn’t have a means to disconnect the control conductors going to the generator. If you use this switch you should install a service disconnect before the switch. The other model that Generac has listed on that page (Service Disconnect Transfer Switch) might be listed for service equipment but I’m not sure. The Generac reps I have talked to don’t recommend using that transfer switch since the only way to access the service disconnect is to un-bolt and remove the front cover. Apparently many of the users that have used this switch have had inspectors reject the installation.

Curt


Curt Swartz

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,157
Joined: May 2003
Top Posters(30 Days)
BigB 5
Popular Topics(Views)
295,021 Are you busy
226,689 Re: Forum
211,858 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5