Main panel over water meter #47168
01/11/05 11:25 AM
01/11/05 11:25 AM
J
Joey D  Offline OP
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
I have an existing main panel that has the water meter under it about 2ft below and it's off the wall 10 inches. Inspector says to move the panel as the code says it can't be mounted above the water meter. I didn't see it so here I am asking. Thanks.

Work Gear for Electricians and the Trades
Re: Main panel over water meter #47169
01/11/05 11:31 AM
01/11/05 11:31 AM
E
electricman786  Offline
Member
Joined: Sep 2004
Posts: 37
sacramento
Clearence area for Panel is
24" to sides
36" to front
from ground to Panel

Re: Main panel over water meter #47170
01/11/05 11:39 AM
01/11/05 11:39 AM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
110.26 covers clearances about panels. There are two parts: the working clearance in front (30 x 36) and the dedicated space above and below (equal to the footprint from floor to ceiling).


Earl
Re: Main panel over water meter #47171
01/11/05 01:15 PM
01/11/05 01:15 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
It is a violation of 110.26 (3), but You say it is an existing situation

What type of authority does this inspector have that he can have you change an existing condition, or what type of project are we talking about?

Roger

Re: Main panel over water meter #47172
01/11/05 09:49 PM
01/11/05 09:49 PM
J
Joey D  Offline OP
Member
Joined: Oct 2003
Posts: 259
Arlington MA U.S.
I am changing out the panel to a new panel, thats it.

Re: Main panel over water meter #47173
01/11/05 11:28 PM
01/11/05 11:28 PM
R
Roger  Offline
Member
Joined: May 2002
Posts: 1,716
N.C.
Joey, the inspector has a valid stance.

Roger

Re: Main panel over water meter #47174
01/12/05 12:21 PM
01/12/05 12:21 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
File under "why people avoid permits". Tough to say without seeing how obsructed the panel is but I do service upgrades like this all the time and never have I moved the panel location. Burdening the homeowner with an added cost might not be an option for them. Thus they will do nothing or avoid permits altogether. Rule 3 from Mass Elec Code. "Addtions or modifications to an existing installation shall be made in accordance with this Code without bringing the remaining part of the installation into compliance with the requirements of this Code. The installation shall not create a violation of this Code, nor shall it increase the magnitude of an existing violation." Where does this leave us?

Re: Main panel over water meter #47175
01/12/05 01:30 PM
01/12/05 01:30 PM
D
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
If it were anything but a water meter I'd suggest that the plumber violated the code and needed to move the plumbing. That's the position some VERY NICE inspectors have taken in the past. It really shouldn't be too much work to relocate to one side with a 90 degree sweep.

Dave

Re: Main panel over water meter #47176
01/12/05 01:34 PM
01/12/05 01:34 PM
D
Dave55  Offline
Member
Joined: May 2004
Posts: 697
Crystal Lake, Illinois, USA
...or add a couple floor-to-ceiling 2X4s and bring the panel away from the wall a foot or two with a long RMC nipple.

Dave

Re: Main panel over water meter #47177
01/12/05 03:33 PM
01/12/05 03:33 PM
E
Electricmanscott  Offline
Member
Joined: Jan 2002
Posts: 1,457
Holden, MA USA
Dave moving the panel is obviously easy. What about all the airing that has to go back into it. Not likely that it will reach.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
254,531 Are you busy
190,768 Re: Forum
180,490 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.032s Queries: 15 (0.006s) Memory: 1.0226 MB (Peak: 1.1963 MB) Zlib enabled. Server Time: 2019-04-22 16:56:43 UTC