Posts: 1
S
Junior Member
I was wondering if anyone has ever seen a isolated ground receptacle with two grounding screws. I know that they have a grounding screw for the isolated ground conductor, but i was wondering if they make one that has a grounding screw for the other grounding conductor.

Horizontal Ad
Joined: Sep 2003
Posts: 650
W
Member
I have never seen such, and believe that such would be essentially useless.

An isolated ground receptacle is only potentially of use in an environment where there is current flow or electrical noise on the grounding system. For example, even in a _properly_ installed metal raceway system, you almost certainly will have loop paths described through the grounded metal. You will almost certainly have changing magnetic flux coupled through these loops, and thus current flow on the ground system.

I suppose you could also have electrostatic pickup by the ground conductor; a isolated ground conductor surrounded by a metal raceway would be shielded from this.

But in any of these metallic systems, the yoke of the isolated ground receptacle will be properly grounded through the metal receptacle box. No need for a second screw.

Now consider an isolated ground receptacle in a non-metallic box. Clearly the yoke is not properly grounded...but on the other side of the coin, a $0.39 Home Depot special in a non-metallic box essentially has an isolated ground. Use a non-metallic wiring method, and a single receptacle on the circuit, and if the run is back to the main panel, then you have something that is electrically an 'isolated ground' receptacle.

-Jon

Joined: Aug 2003
Posts: 1,374
R
Moderator
Perhaps it is to bond a metal faceplate?


Ryan Jackson,
Salt Lake City
Joined: Dec 2003
Posts: 886
H
Member
No, what for? Mount the receptacle in a metal box and you don't need it. Use a plastic box and you don't need a separate isolated ground or an IG receptacle.

-Hal

[This message has been edited by hbiss (edited 01-06-2005).]


Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
HappyElectrician
HappyElectrician
Penn USA
Posts: 31
Joined: December 2011
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
329,719 Are you busy
254,577 Re: Forum
237,050 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5