#46623 12/28/04 02:01 PM
Joined: Jan 2004
Posts: 615
J
Jps1006 Offline OP
Member
I am looking at 600-amp 120/208 3-phase panel fed with 2 sets of parallel 300 kcmil. The lugs they terminate to are 75C.

Table 310-16 ('99, please excuse the archaic reference)
| 75 C | 90 C |

300 kcmil | 285 amps | 320 amps|
350 kcmil | 310 amps | 350 amps|

Am I right to say that this panel should be fed from 350's because of the temp rating on the lugs?

So if my above suspicions are correct, can I fix it like this:
There is a J-box relatively close to the panel. Can I just remove the 300's back to the J-box and split bolt 350's from the panel to the j-box? I guess that is assuming the lugs on the other side are 90C rated, which come to think about is unlikely.

#46624 12/28/04 02:58 PM
Joined: Apr 2004
Posts: 201
Member
You may be alright the way it is depending on the load. If the calculated load is less than 570 amperes, I do not see a problem with using 240.4(B). By the way, you will not be able to use the 90°C rating of the conductor except for the purpose of derating. I do not believe there is any way you will be able to terminate at anything other than 75°C at that ampacity. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy
#46625 12/29/04 12:36 PM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Just to pick nits.

The temperature rating of the lugs, themselves, is not important. It is the temperature rating of the terminations that is important. The termination includes the lug, the device, and the enclosure. All of these factors are important.

I once had a contractor argue that because the lug supplied in a Square D fusible switch was rated AL90CU he could use the 90C column. But he was wrong. There is no UL Listed (or any other NRTL that I know of) overcurrent protective device with a termination temperature rating in excess of 75C.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Samurai
Samurai
Fl.
Posts: 46
Joined: May 2007
Top Posters(30 Days)
BigB 6
Popular Topics(Views)
295,022 Are you busy
226,690 Re: Forum
211,860 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5