arc fault #46189
12/15/04 05:21 PM
12/15/04 05:21 PM
B
Bert66  Offline OP
Member
Joined: Nov 2004
Posts: 80
Belle Chasse, La. USA
I'm doing a remodel and the inspector is asking about the arc-fault protection. To date I have'nt been hit with them yet this is a first, I must admit that I've been waiting for this day. Not that I've been trying to side step the issue, it just was never pushed hard around here. My understanding is that all of the bedroom circuits need this type of breaker. I'm I missing anything else that I should know on this subject?

Work Gear for Electricians and the Trades
Re: arc fault #46190
12/17/04 03:58 PM
12/17/04 03:58 PM
E
earlydean  Offline
Member
Joined: Dec 2003
Posts: 751
Griswold, CT, USA
All the circuits that feed the bedroom outlets need AFCI protection at the panel.


Earl
Re: arc fault #46191
12/17/04 04:59 PM
12/17/04 04:59 PM
C
Coastal  Offline
Member
Joined: Dec 2004
Posts: 23
Kill Devil Hills, NC 27948
All 15 and 20 Amp, 120 volt Outlets...

This includes switches and smoke detectors; even switches operating an outside light. Make sure that you separate the grounded conductors on 3-way switching in multi-gang boxes when you have AFCI and General lighting in the same box. Joining AFCI protected grounded conductors with non-AFCI will caused the AFCI breaker to "trip". This can be very problematic in a remodel!

Re: arc fault #46192
12/17/04 05:12 PM
12/17/04 05:12 PM
J
jkraft  Offline
Member
Joined: May 2003
Posts: 74
Just received the Dec. issue of Electrical
Contractor magazine. Bottom of page 27, Mr. Flach says the switch does not have to be AFCI protected. In my last code update class the opinion was the the switch did have to be protected.

Re: arc fault #46193
12/17/04 09:53 PM
12/17/04 09:53 PM
R
rlc3854  Offline
Member
Joined: Sep 2004
Posts: 15
Amite, LA
It is my understanding that lighting circuits/switches not controlling receptacles do not have to be AFCI protected in bedrooms nor do smoke detectors. Read the NEC for what the intent of the AFCI as defined and perhaps it will be easier to understand.

Re: arc fault #46194
12/17/04 11:11 PM
12/17/04 11:11 PM
R
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
If you are using the 2002 NEC, then branch circuits that serve the bedroom outlets must have GFCI protection. A switch is not an outlet, but if the switch controls lights, receptacles or other loads in the bedroom, it will be on a bedroom branch circuit and require AFCI protection. If the switch controls loads outside of the bedroom, them AFCI protection is not required by the NEC.
Don


Don(resqcapt19)
Re: arc fault #46195
12/20/04 08:17 PM
12/20/04 08:17 PM
R
RobbieD  Offline
Member
Joined: Feb 2003
Posts: 231
Canada
I wouldn't want anyone to wire a smoke detector to an AFCI breaker in my house let alone anyones. If the breaker works and turns off the circuit, it would have done it because it sensed an overcurrent condition or an arc fault. Hopefully this arc fault that it sensed doesn't start a fire because if you don't have a battery backup in your smoke you might just have a very long sleep.

[This message has been edited by RobbieD (edited 12-20-2004).]

Re: arc fault #46196
12/20/04 09:16 PM
12/20/04 09:16 PM
C
Coastal  Offline
Member
Joined: Dec 2004
Posts: 23
Kill Devil Hills, NC 27948
Quote
I wouldn't want anyone to wire a smoke detector to an AFCI breaker in my house let alone anyones. If the breaker works and turns off the circuit, it would have done it because it sensed an overcurrent condition or an arc fault. Hopefully this arc fault that it sensed doesn't start a fire because if you don't have a battery backup in your smoke you might just have a very long sleep.


Battery backup smoke detectors are and should be a requirement. They are required here, as well as to be interconnected, with any new construction and in a remodel if feasable. If they can't be interconnected, then a hard wired/battery backup detector must be installed in all bedrooms, halls and common areas. If an arc fault occurs on their branch circuit causing a fire, the battery will allow the detector to do its job. If the battery is dead, the detector will have signalled with a "beeping", alerting you to change the battery.

Re: arc fault #46197
12/20/04 09:39 PM
12/20/04 09:39 PM
R
rlc3854  Offline
Member
Joined: Sep 2004
Posts: 15
Amite, LA
Anyone care to post the NEC Article that requires that smoke detectors are required to be hard wired and have battery backup?

Re: arc fault #46198
12/20/04 09:53 PM
12/20/04 09:53 PM
N
NORCAL  Offline
Member
Joined: Sep 2002
Posts: 882
The requirement will be in the building code.

Page 1 of 2 1 2

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 165
Joined: March 2007
Show All Member Profiles 
Top Posters(30 Days)
Admin 7
Popular Topics(Views)
251,653 Are you busy
188,790 Re: Forum
178,505 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.036s Queries: 15 (0.010s) Memory: 1.0235 MB (Peak: 1.1995 MB) Zlib enabled. Server Time: 2018-11-21 08:15:28 UTC