3 phase delta #44740 11/10/04 04:39 PM
Joined: Jul 2004
Posts: 28
K
Kelley Offline OP
Member
I was at a site today (new sewer pump station) that will be supplied from a 3 phase delta. Upon checking the meter socket for power i read 240v to ground on a phase, 0 volts to ground on b phase and 240v to ground on c ph. i get 240 v phase to phase. i dont have much experience on this type of system but i thought b phase was the high leg? i'm a little confused does anyone have an answer as to what i should be reading?

thanks
Kelley

Work Gear for Electricians and the Trades
Re: 3 phase delta #44741 11/10/04 04:57 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Your readings are fine.

You have a 3-phase, 3-wire corner grounded delta system, there is no high leg.

A high leg can be found with 3-phase, 4-wire delta systems.

[This message has been edited by iwire (edited 11-10-2004).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: 3 phase delta #44742 11/10/04 05:10 PM
Joined: Jul 2004
Posts: 28
K
Kelley Offline OP
Member
so 240 to ground on a and c phase is ok. thank you iwire

Kelley

Re: 3 phase delta #44743 11/10/04 07:48 PM
Joined: Apr 2002
Posts: 2,527
B
Bjarney Offline
Moderator
 
For 240V delta, regardless of system grounding method, be aware that it is a serious misapplication to use less than 250V fuses or other than 240V circuit breakers. 120- or 120/240V-rated circuit breakers are not intended to be used with 3-wire delta electric services. [See UL white book.]

Re: 3 phase delta #44744 11/10/04 09:02 PM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
Congratulations! You have found the ONE TIME you fuse/switch the "neutral!"

Re: 3 phase delta #44745 11/10/04 10:40 PM
Joined: Nov 2000
Posts: 2,148
R
resqcapt19 Offline
Member
John,
You can't use a fuse in this grounded conductor unless the fuse is used for motor overload protection. You treat this grounded conductor just like any other white wire.
Don


Don(resqcapt19)
Re: 3 phase delta #44746 11/12/04 06:39 PM
Joined: Dec 2001
Posts: 300
M
maintenanceguy Offline
Member
By Bjarney:
____
For 240V delta, regardless of system grounding method, be aware that it is a serious misapplication to use less than 250V fuses or other than 240V circuit breakers. 120- or 120/240V-rated circuit breakers are not intended to be used with 3-wire delta electric services. [See UL white book.]
______

Please explain more.

Re: 3 phase delta #44747 11/12/04 08:58 PM
Joined: Apr 2001
Posts: 518
J
John Steinke Offline
Member
resq- You're quite right- the only times I've encountered this type of power, it was used to power well pumps, and the control voltage came off a transformer.

The UL "White Book" says, under "Circuit breakers, moldes case..." that:
"breakers rated 125/250....are suitable for use....where the voltage to ground does not exceed 125v."
I believe that the "White Book" is available at UL's web site.

Re: 3 phase delta #44748 11/13/04 12:39 AM
Joined: Feb 2003
Posts: 939
F
frenchelectrican Offline
Member
also with delta breaker you can not use the slash on the label like 120/240 volts it must be straght 240 volt becaue of line to ground is pretty high btw it will stated in nec but i cant rember where it is excatally located

merci, marc


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Re: 3 phase delta #44749 11/13/04 07:35 AM
Joined: Apr 2004
Posts: 201
CharlieE Offline
Member
240.85 Applications. A circuit breaker with a straight voltage rating, such as 240V or 480V, shall be permitted to be applied in a circuit in which the nominal voltage between any two conductors does not exceed the circuit breaker’s voltage rating. A two-pole circuit breaker shall not be used for protecting a 3-phase, corner-grounded delta circuit unless the circuit breaker is marked 1–3 to indicate such suitability.

A circuit breaker with a slash rating, such as 120/240V or 480Y/277V, shall be permitted to be applied in a solidly grounded circuit where the nominal voltage of any conductor to ground does not exceed the lower of the two values of the circuit breaker’s voltage rating and the nominal voltage between any two conductors does not exceed the higher value of the circuit breaker’s voltage rating.

FPN: Proper application of molded case circuit breakers on 3-phase systems, other than solidly grounded wye, particularly on corner grounded delta systems, considers the circuit breakers’ individual pole-interrupting capability.


Charlie Eldridge, Indianapolis Utility Power Guy
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Posts: 362
Joined: April 2003
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 15
Popular Topics(Views)
272,103 Are you busy
205,999 Re: Forum
194,033 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3