connection of cooking equipment #44568 11/07/04 09:14 PM
Joined: Nov 2004
Posts: 32
S
sockets Offline OP
Member
What is the usual connection method of commercial cooking equipment in the center of a room. When there is no kneewall.

I saw one example where the wires were in a tubelike flex conduit, which looked strange to me. Perhaps it was temporary or a replacement of equipment required rerouting of power? Odd, what's your opinions?

Work Gear for Electricians and the Trades
Re: connection of cooking equipment #44569 11/07/04 11:52 PM
Joined: Oct 2004
Posts: 5
G
go fetch Offline
Junior Member
power poles, tend to work well

Re: connection of cooking equipment #44570 11/08/04 12:01 AM
Joined: Apr 2002
Posts: 7,113
HotLine1 Offline
Member
Stub-ups, if possible; power poles, or RGC/IMC ceiling to floor flance, with a tee, or box, as required.

If the equip can be cord connected, a suitable cord/twistlock and ceiling mounted receptacle works.

Some fast food ops have a 'cord drop' with matching twistlocks, or pin-sleeve devices.
(Let's not debate cord usage here guys)

John


John
Re: connection of cooking equipment #44571 11/08/04 10:03 AM
Joined: Oct 2004
Posts: 16
C
chimo Offline
Member
As someone who worked in fast-food (yikes!) for years, go with the ceiling drop cords. We had those, the floor junction boxes, & the poles. The floor boxes provide a fantastic fireworks display when mopping, and both pole & floor boxes are easily destroyed when moving equipment around. We finally installed ceiling drops with (quick disconnects?) - they were the only reliable & safe connection.

Re: connection of cooking equipment #44572 11/08/04 06:22 PM
Joined: Nov 2004
Posts: 32
S
sockets Offline OP
Member
The kitchen had an original build date of 1980, do you suppose it had any equipment replacements?

It was the standard seen equipment all under a canopy hood.

Re: connection of cooking equipment #44573 11/08/04 08:04 PM
Joined: Feb 2003
Posts: 687
A
Active 1 Offline
Member
For taller equipment like the stand up friges I like the twist rec on the cieling. Strut mounted to the floor and structure with a pipe and a bell box. It can be solid but they are limited to making adjustments to equip. locations. It tame more time to do. If you get some place that gets what ever used eqipment that is on special it's not the best chioce. Before your done they will have replaced the bad equipment with something different. I like the SO twist cord idea. More flexable in layout.

Tom


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
dougwells
dougwells
kamloops BC Canada
Posts: 1,154
Joined: May 2003
Show All Member Profiles 
Top Posters(30 Days)
Admin 5
Popular Topics(Views)
258,752 Are you busy
194,330 Re: Forum
183,788 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3