Underground Long PVC Run #44383 11/02/04 11:49 PM
Joined: Oct 2004
Posts: 53
I
InspectorE Offline OP
Member
I have a long run (1300') of PVC for some decorative lighting along a driveway. The lamps will be spaced about 130' apart. I'm wondering what the experience is regarding expansion/contraction of the PVC conduit. I know the temp down at 4' or so is pretty constant, but at 2' I'm not so sure it's constant. I certainly don't want any fittings to pull apart. Above ground, expansion fittings would be mandatory.

Work Gear for Electricians and the Trades
Re: Underground Long PVC Run #44384 11/03/04 12:16 PM
Joined: Aug 2004
Posts: 54
G
goodwill Offline
Member
InspectorE,
300.5(J) ground movement,
and 300.7(B) expansion fittings.
I'm assuming that you are in a zone 3 or 4.(did a google on "frost zones")
I personally probably would not bother with the expansion fittings if you can get down to 48"...like you said, it should stay a constant 55°
anything less than 4', I would put one every 50-100'. 352.44(A) (let's say in the summer the earth is an even 55°, and in the winter it is 32°., so 1.01 inches per 100'.)

Re: Underground Long PVC Run #44385 11/03/04 07:00 PM
Joined: Jun 2003
Posts: 681
P
PCBelarge Offline
Member
for conduit that is buried, you will not have to be concerned about expansion fittings.

Pierre


Pierre Belarge
Re: Underground Long PVC Run #44386 11/03/04 10:12 PM
Joined: Apr 2002
Posts: 7,216
HotLine1 Offline
Member
Check Carlon literature, UG is OK without exp. joints. But, you must be stubbing 'up' at the fixture locations, No??

You may get ground heaving conditions by/at the stubs.

BTW, if you have concern, I do not know of any prohibition (NEC) or mfg that says you cannot install exp joints if you want.

John


John
Re: Underground Long PVC Run #44387 11/03/04 11:07 PM
Joined: Oct 2004
Posts: 53
I
InspectorE Offline OP
Member
There will be lantern posts (5' high or so?) every 130'. Since it is underground, it has to be wet rated wire, so I'm not too concerned about any leakage/condensation inside the conduit. Stubs will have to be brought up to the posts, that's correct. Fortunately, the lamps are only 25 w or so, the voltage drop won't be a big factor.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
271,953 Are you busy
205,843 Re: Forum
193,921 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3