Living with NFPA 70E #44380
11/02/04 10:59 PM
11/02/04 10:59 PM
H
hypress  Offline OP
Member
Joined: Jul 2004
Posts: 129
Charleston WV
Has anyone had any experience with NFPA70E the electrical safe work procedures and arc blast protection requirements.From what I have heard some of it is OK but some of it is way out in left field. Our plant has been useing flash suits for switching for years now 70E says you have to use flash suits any time you work on anything 100 volts or more.What is your alls take on 70E. THANKS.

Work Gear for Electricians and the Trades
Re: Living with NFPA 70E #44381
11/03/04 08:22 AM
11/03/04 08:22 AM
B
Big Ed  Offline
Member
Joined: Apr 2004
Posts: 55
Roxboro, NC, USA
Hypress,
It is not as restrictive as that. It stipulates several levels of protection based on the work being done and the voltages present. Basically they have assumed the arc potential for many common jobs and setup the proper protection for each.

I would reccommend that you invest in some arc hazard analysis if you plan on fully implementing 70E, it will significantly lower most of the requirements.

The protection levels can be as low as all-natural fiber clothes up to the full arc suit with ballistic protection.

Good luck,
Ed

Re: Living with NFPA 70E #44382
11/03/04 11:03 AM
11/03/04 11:03 AM
R
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
In order to use the standardized table in NFPA 70E, you must know the calculated fault current at the equipment you will be working on, then calculate the arc flash fault current, then you can match that to the characteristic of the upstream protective deices (breakers and fuses), to see how long it will take to clear the fault. Then and only then can you attempt to use the table in NFPA 70E, if you fall within the parameters of the notes in the table.
I have found many incident energies higher than 40 or even 100 cal/cm^2, thus making any arc suit useless.
Don't forget the energized work permits required by 70E too [Linked Image]
Good luck.


Ron

Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Bill Addiss
Bill Addiss
NY, USA
Posts: 3,903
Joined: October 2000
Show All Member Profiles 
Top Posters(30 Days)
sparky 11
Popular Topics(Views)
250,492 Are you busy
188,052 Re: Forum
177,694 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.015s Queries: 14 (0.004s) Memory: 0.9510 MB (Peak: 1.0751 MB) Zlib enabled. Server Time: 2018-10-20 10:49:13 UTC