#44380 11/02/04 10:59 PM
Joined: Jul 2004
Posts: 129
H
hypress Offline OP
Member
Has anyone had any experience with NFPA70E the electrical safe work procedures and arc blast protection requirements.From what I have heard some of it is OK but some of it is way out in left field. Our plant has been useing flash suits for switching for years now 70E says you have to use flash suits any time you work on anything 100 volts or more.What is your alls take on 70E. THANKS.

#44381 11/03/04 08:22 AM
Joined: Apr 2004
Posts: 55
B
Member
Hypress,
It is not as restrictive as that. It stipulates several levels of protection based on the work being done and the voltages present. Basically they have assumed the arc potential for many common jobs and setup the proper protection for each.

I would reccommend that you invest in some arc hazard analysis if you plan on fully implementing 70E, it will significantly lower most of the requirements.

The protection levels can be as low as all-natural fiber clothes up to the full arc suit with ballistic protection.

Good luck,
Ed

#44382 11/03/04 11:03 AM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
In order to use the standardized table in NFPA 70E, you must know the calculated fault current at the equipment you will be working on, then calculate the arc flash fault current, then you can match that to the characteristic of the upstream protective deices (breakers and fuses), to see how long it will take to clear the fault. Then and only then can you attempt to use the table in NFPA 70E, if you fall within the parameters of the notes in the table.
I have found many incident energies higher than 40 or even 100 cal/cm^2, thus making any arc suit useless.
Don't forget the energized work permits required by 70E too [Linked Image]
Good luck.


Ron

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,409 Are you busy
213,482 Re: Forum
200,389 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5