To all who responded to the following post. I made a mistake. We are trying to pull 4 conductors of #4THHN/THWN in 1 inch PVC. Which is the maximum the code will allow.
All othere comments below still apply. I apologize for the incorrect post but it's been one of those days!!!!
Bob
=================================
Has anyone tried to install 4 conductors of # 6 THHN copper in 1 inch PVC. It's approximately a 70 ft run with 3 nineties and two offsets.
My customer had insisted on installing this portion to save money even though I told him to use 1 and 3/4 inch PVC.
I know the code allows up to 4 conductors in 1 inch PVC, and not more than 3 90's. However, I was forced to install two offsets due to knock outs not lining up.
I'm concerned I'll run into major problems when I pull this wire. I may even ask the customer to install 1.5 inch PVC to make it easier.
Ace, what are the conductors feeding and what size overcurrent device are you proposing to use.
You will also have to count your EGC in this conduit fill which would bring a fifth conductor into the picture if we are talking a three phase four wire feeder.