#43928 10/25/04 07:00 PM
Joined: Jun 2004
Posts: 206
C
Member
Bob, you can call me an MOB anytime. Showing off can be a good thing when you are right. 300.5(D)(5) is a good point to remember also.

Al

#43929 10/25/04 09:20 PM
Joined: Jun 2003
Posts: 681
P
Member
The difference of the "THHN or THWN" type conductor is the temperature rating of the conductor for ampacity rating.
If you use the "THHN or THWN" conductor (dual rated conductor) for underground, you can only use the THWN using the 75*C column of table 310.16, even for ampacity adjustment.
Example: 2 AWG THHN is rated for 130 amps at 90*C, 2AWG THWN is rated for 115 amps at 75*C.


Pierre Belarge
#43930 10/25/04 10:42 PM
Joined: Nov 2002
Posts: 558
G
Member
Bob and Roger are actually College students who room together,and hatch this stuff up.

I think they learned it from two other guys named Ed and Bennie,who went to the same College. [Linked Image]

(Ducking for cover)

Russell

#43931 10/26/04 05:01 AM
Joined: May 2002
Posts: 1,716
R
Member
Russell, no need to duck, being put in the same post with these three guys is quite the honor. [Linked Image]

BTW, Bob keeps his side of the dorm room pretty neat. [Linked Image]

Roger

#43932 10/26/04 06:07 PM
Joined: Jun 2002
Posts: 58
E
Member
Per PCBelarge' comments:
don't forget that the "weakest link" in the circuit governs. The terminals at equipment usually are rated at 60oC or 75oC, so that is the limitation on ampacity. i.e. Column to use in Tbl 310-16ff.
(310.15(B)FPN1

#43933 10/26/04 06:21 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Very true energy7, luckily very few items are not marked as 75 C. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#43934 10/26/04 07:38 PM
Joined: Feb 2003
Posts: 687
A
Member
One time a customer did not want to wait for us so he ran 1 1/4 plumbling pvc. Nothing was glued together. He used plumbing elbows for bends. Under a new brick patio and 1/2 wall.

Tom

#43935 11/01/04 06:43 AM
Joined: Aug 2004
Posts: 106
P
Member
The "plumbing pipe" thing happens to me all the time. Customers call me after they have poured the patio and tell me they already installed the pipe for the hot tub to make things "easy" for me. It's usually 1/2 inch plumbing pipe and fittings no where close to where I need them. Thanks for the help!


Power to the people
Page 2 of 2 1 2

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
The Watt Doctor
The Watt Doctor
Humble, TX
Posts: 440
Joined: December 2001
Top Posters(30 Days)
BigB 4
Popular Topics(Views)
303,018 Are you busy
232,125 Re: Forum
216,777 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5