Are IC rated cans acceptable for direct contact with wooden structural members?
Peter
Peter
|
|
|
|
Joined: Dec 2002
Posts: 308
Member
|
No The can must have at least 1/2 inch clearance from any lumber. IC is INSULATION CONTACT.
Edward.
410-66(a) NEC.1996 Recessed portion of lighting fixture enclosures, other than at the point of support shall be spaced at least 1/2 inch from combustible material. Exception: Recessed fixtured identified as suitable for insulation to be in direct contact with the fixture.
Thanks Edward
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Edward
Read the exception you posted.
IC rated recessed housings do NOT require any clearance from combustible material. The paper backing on older insulation is one of the most combustible items you will find in attics.
Curt
Curt Swartz
|
|
|
|
Joined: Aug 2001
Posts: 545
Member
|
Another point, they do not make the smaller 4" cans with the IC rating. I believe it is because they are too small to dissapate the heat.
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Dec 2002
Posts: 308
Member
|
caselec, you are absolutely right. Learn something everyday.
Edward
Thanks Edward
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
They make 4" IC cans, but the housing is 14"X 14"!
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Apr 2002
Posts: 558
Member
|
Mark, You must be thinking of 4” low voltage housings. Halo, Juno, Lightolier, Nora, DMF, Elco, Etc make 4” line voltage IC housings that are not much larger than the equivalent TC versions.
Curt
Curt Swartz
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Curt, you're right they them... Only minorly larger than non-ic for the line voltage ones. I was stuck in 1499 world there for a while.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|