150 service with 200 panel #41202 08/17/04 05:40 PM
Joined: Aug 2004
Posts: 69
N
nov Offline OP
Member
I wanted to know if there is any reason why I can not put a 200 amp main lug panel in this situation. There is currently a 150 amp main lug panel in place with about five double taps. The main disconect 150 amp is outside next to the meter. this would give me another 10 spaces

Work Gear for Electricians and the Trades
Re: 150 service with 200 panel #41203 08/17/04 09:11 PM
Joined: Apr 2002
Posts: 914
E
Electric Eagle Offline
Member
Nothing wrong with it at all as long as the load being served isn't too much for the 150 amp main. An easier way might be to just add a sub panel next to the main panel.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
HotLine1
HotLine1
Brick, NJ USA
Posts: 7,225
Joined: April 2002
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 15
NORCAL 10
Popular Topics(Views)
274,037 Are you busy
207,809 Re: Forum
195,507 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3