can lights #4098 09/09/01 07:54 PM
Joined: Jun 2001
Posts: 141
A
amp-man Offline OP
Member
Hey y'all,

Just did a job replacing flourescent lights in a kitchen with can (recessed) lights.

These are IC-rated housings (Junos). Because of the layout, two of the housings were installed snug against a joist. Also I used the Arlington black plastic button Romex clamps rather than metal clamps.

I figured that if the cans are safe to bury in insulation, it doesn't matter if they're up against a joist. What do you think?

Also, a guy at my supply house made the comment that the thermal cutoffs for cans are unnecessary now because of a change in the way insulation is made (the guy claimed that insulation used to have a trace of oil in it). He said that he's known electricians who bypassed the thermal cutoff if the fixture was routinely cutting off...
The whole line seemed like bull to me. Anyone who'd bypass a thermal cutoff seems to be putting the residents at risk from fire. Any comments?

Work Gear for Electricians and the Trades
Re: can lights #4099 09/09/01 08:21 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Myself i've about had it up to my eyeballs with supply house guru's, most of which know all about our trade but do not practice it in the field.

they remind me of the old addage, some people work harder at avoiding work than working itself.

Re: can lights #4100 09/09/01 09:17 PM
Joined: Mar 2001
Posts: 2,056
R
Redsy Offline
Member
It seems that 410-66(a)(2) provides approval for your installation.
As far as bypassing a thermal safety device, it is not only un-ethical, it borders on criminal!

Re: can lights #4101 09/09/01 11:53 PM
Joined: Jun 2001
Posts: 642
N
nesparky Offline
Member
bypassing a thermal overload is like putting a penney in an old fuse holder dumb-dangerous-stupid. any electrician who does so deserves to lose his/her license.


ed
Re: can lights #4102 09/23/01 11:46 AM
Joined: Sep 2001
Posts: 19
D
DUBLIN Offline
Member
First of all DO NOT bypass the thermal the Juno IC rated can is UL listed as an assembly and under no circumstances should be removed or altered. In answer to the second Question (can this fixture be installed in direct contact with combustible materials)(the Joist). Yes if it is a Juno IC rated Air-Loc ready style recessed no other Juno recessed fixtures are allowed within 1/2 in. to combustibles.


Work smarter not harder [Linked Image]


| )ubli| |

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
watersparkfalls
watersparkfalls
Washington...Not DC
Posts: 236
Joined: March 2005
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,742 Are you busy
204,967 Re: Forum
193,087 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3