#40463 07/20/04 11:06 PM
Joined: Jan 2004
Posts: 171
M
Merlin Offline OP
Member
Does anyone know the standard for installing an emergency shut off at fuel pumps. I'm not talking about a gas station. This is at my work (stone quarry- per MSHA regulations). I need to install one at our fuel pumps to meet our safety department requirements. I have never installed any hazarous location equipment, so I'm not up on the standards.

Also any information on how this is typically done in a simple way. We have two pumps that need to simultaneously shut down on contact.

Thanks for any information.

#40464 07/21/04 06:14 AM
Joined: Jul 2002
Posts: 680
W
Member
I've seen it done many ways but a 3 pole relay interupting the sub panel feeding the pumps works well. Making sure you interupt all conductors but grounding conductor. In your case assuming they are running off 110v you could get 2 normally closed 2 pole relays and use a panic button to open them. Mount the equipment in an area that isn't hazardous. Their is a standard on the panic button, has to be so many feet from but not exceed ??

[This message has been edited by walrus (edited 07-21-2004).]

#40465 07/23/04 07:58 PM
Joined: Jun 2004
Posts: 7
J
Junior Member
The reference for the emergency stop button is 514.11(C) 2002 NEC. More than 20 feet and less than 100 feet from the despensers.

#40466 07/23/04 09:05 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I work around mines & quarries on occaision & my advice to you is to ask your Federal MSHA inspector for advice. After all, if you get this wrong, he's the one who will cite your company.

I've found most MSHA inspectors to be very knowledgeable about Federal mining laws, to the point that if they cite you, you will likely lose on appeal. They are, however, very weak on the NEC, so try to comply with their requirements first, then comply with the NEC.

Or, you could try their web site
http://www.msha.gov/ComplianceAssistance.HTM

Tom

[This message has been edited by Tom (edited 07-23-2004).]


Few things are harder to put up with than the annoyance of a good example.

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Top Posters(30 Days)
dsk 7
Popular Topics(Views)
284,754 Are you busy
217,367 Re: Forum
203,709 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5