fire alarm relay for elevator #40002 07/10/04 12:17 PM
Joined: Jul 2004
Posts: 3
E
estman Offline OP
Junior Member
hello everyone,

I am putting together a fire alarm system.
The panel is an edwards 2414 which is a basic analog one. my question is how I Interface it with the elevator for a recall?
Thanks,
estman

Work Gear for Electricians and the Trades
Re: fire alarm relay for elevator #40003 07/10/04 12:34 PM
Joined: Feb 2004
Posts: 74
C
CRM Offline
Member
The fire alarm panel will have a combination NO/NC alarm contacts. I would use the NO contacts and connect these back to the elevator control panel. The elevator company will show you where to wire into their panel. So when there is an alarm a set of contacts will close, operating the elevator recall at the elevator control panel.

Re: fire alarm relay for elevator #40004 07/10/04 02:51 PM
A
Anonymous
Unregistered
Here's another idea.
I would not recall the elevator on general alarm. I would use a relay type base for the smokes in the elevator lobbies. Wire the relays in parallel so that a fire in any lobby but the main entrance lobby sends the car to first floor (primary) and a fire in the main entrance lobby will send the car to a different floor. (alternate) Also if your shunting the power to the elevator machine room with a heat detector just use a two pole heat using one side for fire alarm and the other side for shunt. Is the building sprinked? It will make a difference on the detection you put in the shaft. You may want to read through NFPA 72 3-9.3 (1999) and a call to the elevator inspector might be worth it. Since, in my area anyway each inspector seems to want it set up a little differently.

Re: fire alarm relay for elevator #40005 07/14/04 02:09 AM
Joined: Jul 2004
Posts: 3
E
estman Offline OP
Junior Member
thank you guys your answers shed light in my questions.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Potseal
Potseal
Saskatchewan
Posts: 264
Joined: February 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,206 Are you busy
206,091 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3