2" KO in panel among smaller KO's #39943 07/08/04 08:31 PM
Joined: Apr 2001
Posts: 83
D
donles Offline OP
Member
I'm upgrading a service and running new 2" pvc through the foundation wall. The panel is actually a subpanel because the main is pole-mounted 150' from the dwelling. If I run pvc straight to the sidewall of the panel enclosure (what's a better name for this?) it is an area populated with 1/2 KO's, closed of course and not likely to be used in the future. I'd like to locate a 2" conduit hole in this area. Is this kosher? I could make the hole and sandwich ko reducers to avoid having the smaller ko's drop out or to cover the holes in case they do.
My other option is to offset higher up on the side with 45's.
I'm going to look this up to see if the NEC specifically addresses it.
Don

[This message has been edited by donles (edited 07-08-2004).]

[This message has been edited by donles (edited 07-08-2004).]

Work Gear for Electricians and the Trades
Re: 2" KO in panel among smaller KO's #39944 07/08/04 08:48 PM
Joined: Aug 2003
Posts: 1,374
R
Ryan_J Offline
Moderator
I would say do it with reducing washers and you'll be fine. [Linked Image]


Ryan Jackson,
Salt Lake City
Re: 2" KO in panel among smaller KO's #39945 07/08/04 08:49 PM
Joined: Mar 2004
Posts: 98
O
OreElect Offline
Member
Sounds like you need a Electrician.

Re: 2" KO in panel among smaller KO's #39946 07/08/04 09:42 PM
Joined: Nov 2003
Posts: 269
E
electricman2 Offline
Member
He is one according to his profile.


John
Re: 2" KO in panel among smaller KO's #39947 07/08/04 10:23 PM
Joined: Apr 2002
Posts: 558
C
caselec Offline
Member
What size wire are you going to be pulling? It sounds like you are planning on entering the panel (loadcenter) opposite the branch circuit breaker area. If that is the case there isn’t enough wire bending room for large wire. You should either offset the conduit to enter the top or bottom of the side or install a pull can beside the panel to offset the wire into the correct area of the panel.

Edited to add NEC reference. See 408.35

Curt


[This message has been edited by caselec (edited 07-08-2004).]


Curt Swartz
Re: 2" KO in panel among smaller KO's #39948 07/09/04 03:32 PM
Joined: Apr 2001
Posts: 83
D
donles Offline OP
Member
Ryan_J and caselec

Thank you for your opinions and the code reference. I'll use 45's.

This forum is a pleasure to read and take part in due to helpful and considerate members such as you. That is true 99% of the time.
'nuf said.
Don


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
CDS
CDS
Nicholson Ga
Posts: 34
Joined: June 2006
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,034 Are you busy
205,039 Re: Forum
193,154 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3