#39479 06/21/04 04:59 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
Please explain the difference between an insulated and an isolated ground line. Are they not one and the same?

#39480 06/21/04 05:10 PM
Joined: Sep 2001
Posts: 806
N
Member
An insulated ground is just that, an insulated (green) ground wire.

An isolated ground wire is a ground wire that runs all the way back to the service ground, without being connected to raceways or boxes along the way. Occasionally used with sensitive electronic equipment to provide a "clean ground" in electrically noisy environments.

#39481 06/21/04 09:41 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
The code requires an insulated ground in each receptacle found in a patient care area. If I connect this to a dedicated ground from the panel, then its basically an isolated ground is it not? I don't see the wisdom in simply tying off the insulated ground from the receptacle to the nearest j-box ground. What would be the point of having an insulated ground then?

#39482 06/21/04 11:08 PM
Joined: Apr 2004
Posts: 349
Member
Actually, it is not. When you install an isolated ground conductor and utilize an IG receptacle, the ground prong does not connect to the metalic strap of the receptacle. So, when using an IG receptacle, you need 2 grounds: an insulated green equipment grounding conductor to connect the raceway / outlet box / metalic strap of the receptacle, and a separate isolated ground conductor connected only to the receptacle's ground connector (and run back to the main as NJWirenut said).

The idea is to separate the receptacle's ground connection from the 'dirty' equipment ground.

Hope that helps some.
Radar


There are 10 types of people. Those who know binary, and those who don't.
#39483 06/22/04 08:28 AM
Joined: Jan 2003
Posts: 73
C
Member
Sandro

Section 24 of your code book covers this.
If you go to "Appendix B" and look up the rule number,it explains the intent of the rule.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Top Posters(30 Days)
Admin 14
Trumpy 10
Popular Topics(Views)
280,409 Are you busy
213,482 Re: Forum
200,389 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5