insulated and isolated. #39479 06/21/04 04:59 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
Please explain the difference between an insulated and an isolated ground line. Are they not one and the same?

Work Gear for Electricians and the Trades
Re: insulated and isolated. #39480 06/21/04 05:10 PM
Joined: Sep 2001
Posts: 806
N
NJwirenut Offline
Member
An insulated ground is just that, an insulated (green) ground wire.

An isolated ground wire is a ground wire that runs all the way back to the service ground, without being connected to raceways or boxes along the way. Occasionally used with sensitive electronic equipment to provide a "clean ground" in electrically noisy environments.

Re: insulated and isolated. #39481 06/21/04 09:41 PM
Joined: Dec 2001
Posts: 444
S
Sandro Offline OP
Member
The code requires an insulated ground in each receptacle found in a patient care area. If I connect this to a dedicated ground from the panel, then its basically an isolated ground is it not? I don't see the wisdom in simply tying off the insulated ground from the receptacle to the nearest j-box ground. What would be the point of having an insulated ground then?

Re: insulated and isolated. #39482 06/21/04 11:08 PM
Joined: Apr 2004
Posts: 349
Radar Offline
Member
Actually, it is not. When you install an isolated ground conductor and utilize an IG receptacle, the ground prong does not connect to the metalic strap of the receptacle. So, when using an IG receptacle, you need 2 grounds: an insulated green equipment grounding conductor to connect the raceway / outlet box / metalic strap of the receptacle, and a separate isolated ground conductor connected only to the receptacle's ground connector (and run back to the main as NJWirenut said).

The idea is to separate the receptacle's ground connection from the 'dirty' equipment ground.

Hope that helps some.
Radar


There are 10 types of people. Those who know binary, and those who don't.
Re: insulated and isolated. #39483 06/22/04 08:28 AM
Joined: Jan 2003
Posts: 73
C
CDN_ELECTRICIAN Offline
Member
Sandro

Section 24 of your code book covers this.
If you go to "Appendix B" and look up the rule number,it explains the intent of the rule.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,021 Are you busy
205,021 Re: Forum
193,132 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3