Are there requirements where steel flexible conduit has to be used over Aluminum? Is steel considered ridgid?
The Golden Rule - "The man with the gold makes the rule"
|
|
|
|
Joined: Dec 2003
Posts: 886
Member
|
None that I can think of other than maybe environmental.
Both are FMC or Greenfield so no, steel is not rigid.
-Hal
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
Aluminum is lighter and cheaper than steel. Steel is stronger, more abuse resistant. What are the conditions of use at your installation? Unless the engineer specifies steel, 99% of the time, aluminum will be chosen because of the lighter weight (easier installation) and lower cost.
Steel flex is still flexible and not rigid. Rigid is schedule 80 PVC, schedule 40 PVC, heavy wall metal conduit or intermediate metal conduit. Even though Electrical Metallic Tubing (EMT) seems to be rigid, nowhere is it refered to as a rigid conduit.
Earl
Earl
|
|
|
|
Joined: Apr 2004
Posts: 349
Member
|
Pay attention to job specifications, if there are any. In many specs, especially public works, steel flex is specified, and therefore aluminum flex would not comply. Remember, engineers do not have to install the stuff.
One other issue, there are cities in and around the Los Angeles area where approved types of aluminum flex conduit can be utilized as the grounding path, even when the length exceeds 6'. I believe it's 100' for 1/2" Al-Flex, less for 3/4", and less again for 1".
There are problems with the interpretation of this ruling, and it does not apply in all cities. Without saying this is a good or bad idea, many local contractors take advantage of the savings by not providing ground wires when installing Al-Flex.
Radar
There are 10 types of people. Those who know binary, and those who don't.
|
|
|
|
Joined: Apr 2003
Posts: 139
Member
|
Another consideration is that AL is not magnetic and you will not have issues such as Hyteresis.
Bryan P. Holland, ECO. Secretary - IAEI Florida Chapter
|
|
|
|
Joined: Apr 2002
Posts: 914
Member
|
But the Aluminum stuff will turn your hands black and everything you touch. For that reason I prefer the steel.
|
|
|
|
Joined: May 2004
Posts: 73
Member
|
You also can't use some of the set screw connectors, probably cuz they punch a hole in it
|
|
|
|
Joined: Dec 2003
Posts: 524
Member
|
... Also, with aluminum,you have to use an "MC" type connector,where the binding screw won't pierce the jacket,..with steel, you can use the standard "Bx" connector.. Russ
.."if it ain't fixed,don't break it...call a Licensed Electrician"
|
|
|
|
Joined: Dec 2003
Posts: 524
Member
|
.."if it ain't fixed,don't break it...call a Licensed Electrician"
|
|
|
|
Joined: Dec 2000
Posts: 4,294
Member
|
Radar, Is the Aluminum flex still OK as a grounding path in LA?? Somewhere I've got a "square cutter", a tool that was used to hold flex so it could be cut with a hacksaw. It seems like that was a requirement for using the flex as a ground. I haven't used it in about 20 years.
|
|
|