Can pentrox be used to connect two dissimmilar metals?

Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Aug 2003
Posts: 1,374
R
Moderator
110.14 Electrical Connections.
Because of different characteristics of dissimilar metals, devices such as pressure terminal or pressure splicing connectors and soldering lugs shall be identified for the material of the conductor and shall be properly installed and used. Conductors of dissimilar metals shall not be intermixed in a terminal or splicing connector where physical contact occurs between dissimilar conductors (such as copper and aluminum, copper and copper-clad aluminum, or aluminum and copper-clad aluminum), unless the device is identified for the purpose and conditions of use. Materials such as solder, fluxes, inhibitors, and compounds, where employed, shall be suitable for the use and shall be of a type that will not adversely affect the conductors, installation, or equipment.


Ryan Jackson,
Salt Lake City
Joined: Apr 2002
Posts: 914
E
Member
According to the manufacturer (FCI Burndy) Penetrox is UL listed for aluminum to copper connections. http://ecatalog.fciconnect.com/fci/datasheet.asp?PN=PENA3a&FAM=Penetrox&P=127610,127601