ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photo of the Week:

Multi Meter Service
Multi Meter Service

Advertisement:-Left
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 80 guests, and 21 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#37633 04/30/04 09:55 PM
Joined: Apr 2004
Posts: 4
T
Junior Member
Need some advice. I've got bedroom outlets that are wired using 14/3 romex. When I replaced the regular two pole breaker with a 2-pole arch fault,the circuit fed by the red wire trips the arch fault. When I dissconnet the branch circuit from the homerun, breaker holds. Both circuits have lights and outlets combined. This is my first dealing with arch fault. I want to know if there are certain devices that cannot be protected by an arch fault breaker. Any advice would be appriciated. Thanks

Horizontal Ad
#37634 04/30/04 10:13 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
AFCI's, like GFCI's, don't get along well with multiwire circuits. You need another nuetral.


Ryan Jackson,
Salt Lake City
#37635 04/30/04 10:31 PM
Joined: Apr 2004
Posts: 4
T
Junior Member
Do I need a second neutral parallel to the 14/3 homerun?

#37636 04/30/04 11:42 PM
Joined: Apr 2002
Posts: 558
C
Member
Oops……I miss read your first post that you were using a 2-pole AFCI.


[This message has been edited by caselec (edited 05-01-2004).]


Curt Swartz
#37637 04/30/04 11:58 PM
Joined: Mar 2004
Posts: 9
S
Junior Member
Are you positive you have the two hots that share the grounded conductor? Or if anywhere else in the home you have the grounded conductor of more than one cir (not your 14/3 cir but a differnt one), in say a two gang switch box and they are all tied together it would trip your two pole AFCI.

[This message has been edited by samster (edited 05-01-2004).]

#37638 05/01/04 12:09 AM
Joined: Apr 2004
Posts: 4
T
Junior Member
Do you mean neutrals, when you said grounds? That might be my problem.

#37639 05/01/04 12:40 AM
Joined: Apr 2002
Posts: 558
C
Member
Did you connect the neutral from the 14-3 to the AFCI or is it still connected to the neutral buss in the panel? If it is connected to the breaker you probably have a ground fault on the neutral somewhere in the circuit or another circuit is sharing one of your circuit conductors. Disconnect all 3 of your circuit wires in the panel and check continuity between each wire and ground. DO THIS WITH ALL POWER TURNED OFF NOT JUST YOUR CIRCUIT! If any wire shows continuity to ground you have a problem and need to start searching.

Curt


Curt Swartz
Horizontal Ad
#37640 05/01/04 01:50 AM
Joined: Feb 2004
Posts: 1,438
Member
Most common problem I've come across when retrofitting ACFI's in is that the bare ground wire is touching a neutral terminal on a receptacle someplace... You might have a bit of troubleshooting... One way to tell is to 1) unplug everything connected to the problem circuit, turn off all light fixtures. 2) install a regular breaker for the same circuit
3) disconnect the neutral from the panel, cap it off & leave the ground connected 4) restore power & use a plug in tester on the problem circuit... If it doesn't show "Open Neutral" then you have a ground & neutral in contact someplace.. Or possibly, as Samster pointed out, a box where a neutral from another circuit leading to the panel & is tied together (paralleling) back to the panel neutral bar.. (typically would be found in 2 gang switch/recept locations where the lighting & recept circuits are separate)
Hope this helps [Linked Image]

-Randy

[This message has been edited by Lostazhell (edited 05-01-2004).]

#37641 05/01/04 10:49 AM
Joined: Apr 2002
Posts: 558
C
Member
Randy

Since this is a multi-wire circuit I wouldn't recommend energizing it with the neutral disconnected. Doing so could be very expensive.

Curt


Curt Swartz
#37642 05/01/04 03:24 PM
Joined: Apr 2004
Posts: 9
N
Junior Member
Why are you installing an Arc Fault breaker. Here in Michigan we only have to install it on new installations. Are they making you do it on existing circuits? What a pain in xxx

Nick

Page 1 of 2 1 2

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
noderaser
noderaser
Portland, Oregon, United States
Posts: 404
Joined: March 2007
Top Posters(30 Days)
Popular Topics(Views)
333,621 Are you busy
258,986 Re: Forum
240,408 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5