#36771 04/14/04 11:23 AM
Joined: Feb 2004
Posts: 2
S
Junior Member
Is it permitted to installed a duplex receptacle under a raised floor and pass a cord through the tile to feed a workstation?
(This is not an enviromental air plenum)

#36772 04/14/04 02:37 PM
Joined: Jun 2003
Posts: 1,143
D
Member
Good question.

Is this one of those "tile" type floors like you have in computer rooms? I would think that the AHJ would prefer the receptacle to be mounted on or above the finish (raised) floor, for easier inspection/access.

If I was faced with this situation, I'd probably surface mount a J-box (or dedicated duplex box) to the tile, and attach that to the existing "sub" (real) floor mounted raceway system by means of MC/flex.

The closest ref. I can find is Underfloor Raceways (390).

When in doubt... ask your AHJ?!

#36773 04/14/04 04:28 PM
Joined: Aug 2003
Posts: 1,374
R
Moderator
400.8(2).


BTW: I'm a big fan of your music [Linked Image]


Ryan Jackson,
Salt Lake City
#36774 04/14/04 04:53 PM
Joined: Mar 2002
Posts: 582
R
Ron Offline
Member
The general answer is as stated by Ryan. There is a possibility that this can be done if you are in compliance with Article 645, and the cord is listed as Data Processing Cable.


Ron
#36775 04/15/04 03:44 PM
Joined: Feb 2004
Posts: 2
S
Junior Member
Thanks to all, additional comments are welcome.

#36776 04/15/04 03:56 PM
Joined: Jun 2003
Posts: 1,143
D
Member
Good eye, Ryan!


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
timmp
timmp
Leo, IN, USA
Posts: 28
Joined: June 2004
Top Posters(30 Days)
dsk 6
Popular Topics(Views)
284,726 Are you busy
217,350 Re: Forum
203,701 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5