37
9
I recently purchased a house that I am fixing up for resale. I upgraded the service to 200amps and installed new main distribution panel. Approx 70% of the house has been rewired and is being fed by the new panel. Six existing 20 amp circuits are being fed by a federal pacific sub-panel.
For obvious reasons I want to replace the FPE Panel. I want to run these six circuits back to my new main panel rather than replacing the sub-panel. The new panel located 20’ away on the exterior of the house.
I would delete the sub-panel, splice the conductors and run them to the new panel in 1’ EMT
Here are the questions:
Can I just run # 12 THHN for each of these circuits or do I need to derate?
Are there any other pitfalls to this plan??
I see no problem with that plan as long as you'll have a total of 9 wires (2 hots to 1 neutral). I've seen some people here call them edison circuits. NEC calls them multiwire branch circuits and where I come from they call them networks.
If you aren't familiar with these types of circuits and the hazards of wiring them incorrectly then don't do it. You would need (12) wires in which case you'd need to derate.
BTW you could fit those in 3/4" EMT.
i would also add a ground wire for the circuits and pigtail a jumper the junction box(if metal). i'm not sure if one ground wire would be enough for all 6 circuits
The extra ground wire is really not necessary, but couldn't hurt. One ground wire would be enough for 6 circuits or 60 circuits.
... Even if he pulls (9) wires in that pipe, doesn't he still have to derate,being that there are more than (3)current carrying conductors in that raceway??? Russ
I don't have this suff memorized but I'll have a go... 3-6 80% 7-9 70% 10- ?? 50%
but table 310-16 says # 12 copper thhn is rated for 30 amps. meaning you can put (30 amps times 70% = 21 amps) 21 amps.
The note at the bottom the table is for overcurrent protection.
NEC 99
Okay I did have to look up the table.
Attic Rat
You are correct. If these circuits are multi-wire circuits the neutrals don’t need to be counted but there will still be 6 current caring conductors. The ampacity of #12 THHN is 30 amps and table 310.15(B)(2)(a) specifies 80% adjustment factor for 4-6 conductors. This would result in the #12 THHN conductors having an ampacity of 24 amps. If these wires are installed in wet locations the starting ampacity of #12 THWN in 25 amps which after applying would result with an ampacity of 20 amps.
Curt
Curt Swartz
...Thanx guys,.. ![[Linked Image]](https://www.electrical-contractor.net/ubb/smile.gif) Jsimontucson,..watch your phasing when using (1)neutral per (2)hots...make sure that each corresponding phase conductor lands on a different phase...otherwise unfavorable imbalances on the neutral leg will result in overheating the neutral..Just group your breakers accordingly..."A" phase for one phase conductor,..and "B" phase for the other, and land the neutral normally.. Russ [This message has been edited by Attic Rat (edited 03-28-2004).]
Why not run ONE neutral, and ONE ground, using the stock neutral and ground bussbars in the original panel? (of course, the neutral appropriately sized)
Thank you all verry much for your help.
[This message has been edited by jsimontucson (edited 03-29-2004).]