Listed Hardware for Landing Lugs as GND? #35572 03/14/04 11:33 PM
Joined: Mar 2004
Posts: 32
C
CalSparky Offline OP
Member
I have a metalic enclosure sandwiched between RNC. I'd like to use a two-terminal landing lug to serve not only as my grounding means but to also splice the grounds (splicing SE cable to THHN). My question is: "Can I use standard bolts, lockwashers, and nuts to fix the lug to the enclosure or must I use some sort of listed components (i.e. specialized nuts, bolts, and washers)?". According to 250.8 (2002 NEC) the stuff must be listed but the folks that I've been talking to have said that standard hardware is good 'nough. My common sense says that standard hardware with lock washers should hold for eternity but I'd like more feedback. I've left messages for the local inspectors without a word back. Any help is appreciated.
By the way, if someone out there has had success with something other than a landing lug, please let me know -- Thanks.

Work Gear for Electricians and the Trades
Re: Listed Hardware for Landing Lugs as GND? #35573 03/14/04 11:45 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline
Member
If i am understanding you correctly?
I have done that installation many times and inspection has passed with out any Ifs, Ors and Buts.
However, i am sure you know this the paint of the enclosure must come off first. The lug must make a good mechanical contact with the enclosure.

Edward

PS. where abouts are you in N.Cali.


Thanks
Edward
Re: Listed Hardware for Landing Lugs as GND? #35574 03/14/04 11:49 PM
Joined: Nov 2002
Posts: 244
W
wewire2 Offline
Member
Standard hardware is OK. Scrape the paint off in the area under the lug. Apply Noalox or coppercoat to make a better connection and
stop rust. I use Stainless.

Re: Listed Hardware for Landing Lugs as GND? #35575 03/15/04 12:05 AM
Joined: Mar 2004
Posts: 32
C
CalSparky Offline OP
Member
Thanks for the feedback!
Yea .. on the paint thing I have had success with removing strips of paint by lightly letting my cordless drill "dance" accross the metal with a metal drill bit. Are strips good enough (something tells me "no") or should there not be a stitch of paint under the lug?

P.S. Northern Sacramento (Roseville-Rocklin area)

Re: Listed Hardware for Landing Lugs as GND? #35576 03/15/04 01:18 AM
Joined: Dec 2002
Posts: 308
E
Edward Offline
Member
A drill bit does not work as well as a filler. it is a small 1/4 inch shaft with teeth at the end and on the sides. It is a round file which can be used on a drill motor. It works great.
I would take off paint larger than the area of the lug.Get it down to bare metal.

Edward


Thanks
Edward
Re: Listed Hardware for Landing Lugs as GND? #35577 03/15/04 05:32 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline
Moderator
Go to the Big Orange Box store and pick up a wire brush for your cordless @ $2.00 it is worth while, it will clean the paint off of any enclosure for a good contact.

Any nuts and bolts are OK just try to size them to the hole in the lug, not really a code issue but using a 1/4" bolt with fender washers on a lug with a 1/2" hole looks real unprofessional in my opinion not to mention you can get far better clamping pressure with the larger bolt. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Re: Listed Hardware for Landing Lugs as GND? #35578 03/15/04 05:37 AM
Joined: Jan 2004
Posts: 91
R
rizer Offline
Member
absolutely, positively remove all the paint . i was called out to a womans home who was getting shocked by her dryer.(1989).
i looked at her panel and found the ground wire had been installed on a mechanical lug added to the panel. i turned off the light in the closet and saw a tiny ball of blue flame at the corner of the lug trying to eat a hole through the paint. after removing the paint the problem was solved.

Re: Listed Hardware for Landing Lugs as GND? #35579 03/15/04 08:30 AM
Joined: Dec 2003
Posts: 524
Attic Rat Offline
Member
...What about "tapping" the hole out to accept a 10-32..or 1/4-20 bolt..?? How thick is the enclosure wall??..Granted,paint removal still applies..
Russ

[This message has been edited by Attic Rat (edited 03-15-2004).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Re: Listed Hardware for Landing Lugs as GND? #35580 03/15/04 08:46 AM
Joined: Dec 2003
Posts: 751
E
earlydean Offline
Member
250.8 only covers the lug, which must be listed. The mounting hardware is overlooked.
I asked this question of James Stallcup at a seminar. He said to use stainless with two washers and a locknut. Remove all paint to bare metal. Use an oxide inhibiter like penetrox or copper coat. You may paint the entire assembly, after the inspection.

Earl


Earl
Re: Listed Hardware for Landing Lugs as GND? #35581 03/15/04 11:36 AM
Joined: Mar 2004
Posts: 32
C
CalSparky Offline OP
Member
It turns out that the landing lug has a quarter inch hole, so the 10-32 screw wouldn't work out unless you really torqued it down. Thanks for the feedback (that goes for all)!

Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 9
Popular Topics(Views)
272,071 Are you busy
205,961 Re: Forum
194,010 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3