This picture shows my Volt-tic lit up... touching the PVC drain pipe...
This picture shows the Volt-tic dead an inch away from the PVC to show that it isn't stray voltage making the whole area "hot"...
All the pressurized lines are 0 volts, the tub drain was 32.6V TRMS, the sink drain was 33.4V TRMS, the vent pipe in the attic was 44.2V TRMS.
Bonding the vent pipe would cure the sink, bonding the sink would cure the vent pipe, but the tub had to be bonded separately to show 0 volts.
The PVC in the pictures is between the tub and sink, retrofitted to old galvanized drain pipes in the walls, and the vent pipe in galvanized, but 90's into the chimney chase and and doesn't come back into view until up in the attic.
There are no obvious shorts, I even completely removed the medicine cabinet/ vanity lights...
Bonding seems to "fix" it but I'm afraid of creating a high resistance short that could worsen and cause a fire before it trips anything.
It's an old 60A fuse box...BTW...
I've searched everywhere but the chimney chase, and it would be very invasive to get there...
They want a total service change and rewire this Sept, so can I bond it for now or what?