Oven and cooktop load #35363 03/09/04 07:46 PM
Joined: Feb 2004
Posts: 133
E
Electric Ian Offline OP
Member
Given the following:
Wall mounted oven with nameplate rating of 240V, 8KW, 40Amps.
Cooktop with nameplate rating of 240V, 8KW, 40Amps.
Can I run an #8/3 with 40A OCPD to a JBox. Two whips tapped from the JBox, one to the oven and one to the cooktop. Each whip is #10THHN in greenfield?
Table 220.19 note 4 allows the oven and cooktop to be to have their nameplate ratings added together and treated as one range. Thus I effectively have a range with a 16KW rating. For a 16KW range, table 220.19 note 1 applies. This gives me 8KW+[4(.05*8)] =9.6KW. 9.6KW/240=40Amps. Thus, I should be able to use a 40Amp branch circuit to feed both units. Anyone see any problems with this?

Work Gear for Electricians and the Trades
Re: Oven and cooktop load #35364 03/09/04 08:29 PM
Joined: Sep 2003
Posts: 200
U
u2slow Offline
Member
I'm not familiar with the NEC, but aren't standard breakers only to be loaded to 80%?

So 40A * 125% = 50A

That would require #6 wire running to the JB and 50A OCP.

I would size the conductors running to each unit from the JB as though they were each their own range. (That's probably how you arrived at #10 wire?)

Re: Oven and cooktop load #35365 03/09/04 09:04 PM
Joined: Feb 2004
Posts: 133
E
Electric Ian Offline OP
Member
I believe the 80% rule you refer to is for continuous loads only. I don't believe a range is considered a continuous load.

Re: Oven and cooktop load #35366 03/11/04 07:24 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline
Member
I would run two dedicated circuits 40A each.

That way i know when they have both of the units on during a party or Thanksgiving cookoff they will not trip the breakers.

Edward


Thanks
Edward
Re: Oven and cooktop load #35367 03/18/04 01:53 PM
Joined: Jan 2003
Posts: 73
C
CDN_ELECTRICIAN Offline
Member
I think the approach is wrong, here!

Electric Ian your looking at the rules for "Calculating Demand Factors" which basically used for calculating Total Loads.

Edward is correct, the rules that would apply would be rules that relate to Protection of Conductors and Equipment. (fusing)

Due to this, each unit gets a seperate feed, unless the unit comes with protection for the remote unit buit-in.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,216 Are you busy
206,108 Re: Forum
194,100 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3