First time happening to me. #34733 02/21/04 07:45 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Today i accidently touched hot and the grounded wire. Bam,sparks,smoke...However. the 15Amp breaker did not trip.This is the first time i have seen this happening.

All i could make out from the cover plate:
AMERICAN ELECTRIC or AMERICAN (something)
It started with AMERICAN.

Advised the client to change the subpanel.

Edward.


Thanks
Edward
Work Gear for Electricians and the Trades
Re: First time happening to me. #34734 02/21/04 07:54 PM
Joined: Jun 2003
Posts: 1,143
D
DougW Offline
Member
Wise choice.

Maybe the "grounded" conductor wasn't (at least at the panel) effectively grounded?

Did it pop the OCD at the main panel? (depending on the branch OCD size)

Re: First time happening to me. #34735 02/21/04 09:03 PM
Joined: Aug 2002
Posts: 141
E
elecbob Offline
Member
I frequently have this problem on Federal Pacific and Zinsco panels. Customers freak out when I give them a demostration and I usually end up with a job for a panel change out. As a sidenote: I usually install Square D QO series panels.
Bob

Re: First time happening to me. #34736 02/21/04 09:32 PM
Joined: May 2002
Posts: 1,716
R
Roger Offline
Member
American Electric manufactures replacement or reconditions old breakers for FP panels.

Roger

[This message has been edited by Roger (edited 02-21-2004).]

Re: First time happening to me. #34737 02/21/04 11:49 PM
Joined: Apr 2001
Posts: 507
G
golf junkie Offline
Member
I pinched a wire once with a wireway cover. The #10 THHN burned clean thru, the GE breaker never did trip.

It happens.

GJ

Re: First time happening to me. #34738 02/22/04 09:18 AM
Joined: Sep 2002
Posts: 894
N
NORCAL Offline
Member
There was a company called American Switch later Zinsco/Amercan Switch.

Re: First time happening to me. #34739 02/22/04 05:11 PM
Joined: Nov 2002
Posts: 790
W
wa2ise Offline
Member
Take a look at this web page on FPE "No Trip" brakers.
http://www.inspect-ny.com/fpe/fpepanel.htm

Was that one of these?

My father used to work for Federal in Newark NJ back in the early 1950's doing accounting type work. He used some of their stuff when he built our house, and I don't think he would have used a stab-lok panel if he was aware of any issues with them. That panel got replaced with a Square D QO panel recently.

Re: First time happening to me. #34740 02/22/04 05:30 PM
Joined: Oct 2003
Posts: 289
:
:andy: Offline
Member
why exactly do the FP breakers not trip? what`s the background? Mechanic damage or Production fault?


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
RH1
RH1
California
Posts: 22
Joined: August 2009
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,207 Are you busy
206,095 Re: Forum
194,097 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3