ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
Joined: Aug 2002
Posts: 1,691
S
SvenNYC Offline OP
Member
I've always been leery of the type that uses a set screw to bite down on the armor. I saw three different types today at Lowes.

One was a type that uses metal straps held in place with two screws at opposite ends. Another type is a sort of compression fitting. A third has a saddle (a piece of metal inside the connector body) that clamps down on the armor.

Each of these seem like they avoid damaging the armor. I've always been leery of having the set screw pierce or crush the armor, yet I want to have a good reliable ground connection. [Linked Image]

Joined: Dec 2003
Posts: 886
H
Member
Those old set screw connectors are only good for steel type AC. Nowadays you are likely to run into type MC as well as aluminum armored type AC. To save alot of confusion I only buy connectors listed for all three types, check the box. I'm not familiar with the compression type you saw but the other two sound good.

Joined: Aug 2002
Posts: 1,691
S
SvenNYC Offline OP
Member
HBISS,

The compression connector is a sort of sleeve with a screw on the side. When you tighten the screw the sleeve tightens around the armor.

I liked the design of that one the best because it seems to apply even pressure around the armor, not at one or two points (so it probably won't crush or flatten the armor as easily).

You're right about checking the master-boxes they are shipped in. The individual baggies used to wrap the connectors don't offer much of an explanation.

Joined: Sep 2003
Posts: 200
U
Member
We use the Arlington Snap2it line heavily at work when installation speed is a factor. Otherwise we use the T&B CI70 (single) and CI2175 (duplex).
http://www.aifittings.com/arliprod3.htm
http://www.tnb-canada.com/catalogues/pdf/en/iberville_roughing_in/roughing_01b_eng.pdf

Joined: Aug 2003
Posts: 1,374
R
Moderator
I always used speed locks unless I was doing a cut-in box, in which case I used the one that looks like a romex connector.


Ryan Jackson,
Salt Lake City
Joined: Nov 2002
Posts: 794
Likes: 3
W
Member
Quote
yet I want to have a good reliable ground connection.

Most modern BX has a bare wire runner just inside the armor and outside the paper wrapping covering the white and black wires. As I understand it [Linked Image] you're supposed to take this bare wire and bend it over the antishort you just stuck in so it doesn't fall out, and then wrap the bare wire back around the outside of the armor so it lays in the groove between adjacent wraps of the armor. Then fit the connector over that and clamp it so the litle indents in the clamp clamp that bare wire. That you're not supposed to have any of this bare BX wire inside junction boxes, unlike romex. The metal box is then your ground connection.

Some BX has aluminium armor sheathing, and it says not to use set screw connectors with it.

Why is it that there is no problem with this aluminium armor BX cable with copper wire inside, but aluminium romex wiring caused lots of trouble? The ground has to be able to take a fault current.

Joined: Dec 2000
Posts: 4,294
Member
Combined with the armor, yes, it makes a good ground.

Joined: Jan 2004
Posts: 66
C
Member
heres my theory regarding the aluminum. The main problem with the aluminum is that a very small amount of corrosion increases the resistence slightly. the actually corrosion doesn't cause that much of a problem. However, the heat causes expansion and contraction of the joint. after a while this loosens the connection. thats when the real problems start. In the case of aluminum BX, since there is not normally current flowing in it, the juntions don't experience the heating and cooling that loosens the connections in the current carrying conductors. therefore, even if there is some corrosion, there is still a sufficient ground to trip a breaker in the even of a ground fault.

It's just like steel conduit. it's used for a ground, but when was the last time you saw a steel conductor? (yes, i know some people on here actually have seen them) [Linked Image]

[This message has been edited by cpalm1 (edited 02-16-2004).]

Joined: Dec 2003
Posts: 886
H
Member
The compression connector is a sort of sleeve with a screw on the side. When you tighten the screw the sleeve tightens around the armor.

Yup, I think I know what you are talking about. It's not really a compression connector but just another type of clamp. They have actually been around probably longer than the set screw connector. I kind of like them myself when I can find them. They grab the armor real well.

Joined: Jan 2003
Posts: 4,391
I
Moderator
1 [Linked Image from bptfittings.com]

2 [Linked Image from bptfittings.com]

3 [Linked Image from bptfittings.com]


Bob Badger