I'm bidding a job where I have to install hand dryers in bathrooms. All the bathrooms where I've been, I've never seen a service disconnect. Looks like one would be required, especially in a setting where the breaker may be in a far remote panel, such as the one I'm doing in a large clinic where there is several thousand square feet of space. Maybe it's not required?????? Thanks Steve.....
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
422.31(B) Appliances Rated Over 300 Volt-Amperes or 1/8 Horsepower. For permanently connected appliances rated over 300 volt-amperes or 1/8 hp, the branch-circuit switch or circuit breaker shall be permitted to serve as the disconnecting means where the switch or circuit breaker is within sight from the appliance or is capable of being locked in the open position. Just make sure you provide a lock out kit on the breakers feeding the dryers. Talk to the breaker suppler you can get a lockout kit made for the breaker that stays mounted to it.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
A Burger King restaurant I freuqent has the hand dryer connected to an adjacent GFCI receptacle by a short (1-foot) piece of extension cord. With the ground pin chopped off the molded-on (and scorched) cord-cap. [This message has been edited by SvenNYC (edited 12-22-2003).]
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
iwire, Thanks for the response, I went and got my trusty code book out. I think mine will fall under the one above the article you gave me. Mine will be under 300 volt/amperes or 1/8 Horsepower, so the disconnecting means can be the branch circuit overcurrent device... Thanks for the help. Steve
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Sparky: The ones I remember installing where like 1500VA+
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
SvenNYC, Thanks for the reply, I was sorta thinking on a little more "upgrade quality" than that way though
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Your welcome Steve.
But I do agree with Ryan a hand dryer less than 300VA seems unlikely.
16 amp 120 or 10 amp 240 are both ratings I normally see.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Oct 2002
Posts: 830
OP
Member
|
Ryan, iwire, I'm sure you're probably right, I think I done some wrong figuring here. Thanks for keeping me straight Steve..
|
|
|
|
Joined: Dec 2003
Posts: 524
Member
|
.. A Burger King restaurant I frequent ... ..Sven I'm surprised at you...don't ya know that crap'll kill you..??
.."if it ain't fixed,don't break it...call a Licensed Electrician"
|
|
|
|
Joined: Sep 2003
Posts: 119
Member
|
The hand dryer or the food
Theres always enough room in the junction box.You just need a bigger hammer
|
|
|
Posts: 28
Joined: May 2007
|
|
|
|
|