Comments on the following located at a electrical D-I-Y help site. The author wanted to use the exisiting range circuit for a 120v outlet for use by a new gas stove?
"I removed the 220V receptacle and replaced it with a 110V receptacle. I used the black wire as the hot and the white wire as the neutral. I capped the red (hot) wire and left it in the box. It works like a champ. I have not done anything to the breaker panel yet. It was already too late in the evening to cut the power so I am leaving that part for the morning. I have to take the breaker with me to Home Depot because there are 10 different types of breakers. I will swith the breaker in the morning to the 20A. Just out of curiosity, why does it matter if I leave the 50A breaker there?? "
Rick Miell
|
|
|
|
Joined: Sep 2001
Posts: 806
Member
|
Breaker ratings aside, I would like to know how he terminated the original 50A wiring to a 15 A receptacle.... Here is another , even more worrisome attempt at a similar retrofit, from a recent Usenet post: I have a 220 knob and tube outlet behind my range I need to convert to 110. The wires are in good condition, there are 6 individual wires on the hot, 7 on the neutral and 6 on the ground. I spoke to a contractor and he recommended that I just wirenut off one each of the hots and neutrals, and connect the rest to a normal plug.
My question is, since there are 6 and 7 wires on the hot and neutral, respectively, will it work to just wire nut and tape off 3 and 4, respectively, or does this present problems. If the method above is completely off-base and unsafe that information would also be helpful.
|
|
|
|
Joined: Aug 2002
Posts: 1,691
Member
|
NJWirenut said: Breaker ratings aside, I would like to know how he terminated the original 50A wiring to a 15 A receptacle.... In-wall conductors for 50-amp electric stove circuits are usually stranded right? I'm wondering if the guy actually "trimmed" the conductors by cutting out strands until it was small enough to wrap around the terminal screws of a standard 110-volt socket. This is a gas stove the guy is fitting? I'm wondering if the 110-volt 15-amp supply is for the electric "spark plug" type pilots that some stoves are sold with (instead of standard gas pilots).
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Depending on the model of stove, it may need power for lights and a clock as well. That post about 6 hots and 7 neutrals sounds fascinating. I bet the wiring in that place would make for some interesting ECN threads!
|
|
|
|
Joined: Oct 2000
Posts: 4,145 Likes: 4
Member
|
Paul, My guess would be that the person is talking about wire strands. I'd sure like to have a picture of this completed installation. Bill
Bill
|
|
|
|
Joined: Jul 2003
Posts: 394
Member
|
About terminating 50 A cable on a 15 A plug. Very easy. Bend out one strand and backstab it into the recep.
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
Ah right! I see what he was getting at now. Unfortunately, I've seen similar tricks done here.
|
|
|
|
Joined: Aug 2002
Posts: 1,081
Member
|
How will he trace the strand from the kitchen to the corresponding strand in the panel?
|
|
|
|
Joined: Dec 2001
Posts: 2,503
Member
|
Trial and error. Or he'll rely on the strands making enoughcontact where they touch each other inside the cable However, I'm not really sure he's talking strands. Or why are there 6 on the hot and 7 on the Neutral?
|
|
|
|
Joined: Aug 2001
Posts: 7,520
Member
|
One strand already broken off on the hot wire?
|
|
|
Posts: 30