Torque Frequency #3088 08/05/01 12:11 AM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
How often should Aluminum terminations be retorqued?
I ran into some really nasty ones the other day.

Work Gear for Electricians and the Trades
Re: Torque Frequency #3089 08/05/01 02:49 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
good Q.
it seems on initial installation that i can reef on a termination, and then gain somemore after a few hours.
usually, on a service call, i will give terminations a 'tweek' in a panel, along with sweeping out the dust bunnies, and working the breakers. [Linked Image]

Re: Torque Frequency #3090 08/05/01 05:34 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Never.

If you have some reason to believe the connection is loose, remove the conductor, trim the end back to fresh material & re-install using a torque wrench set to the value listed on the device


Few things are harder to put up with than the annoyance of a good example.
Re: Torque Frequency #3091 08/07/01 02:41 PM
Joined: Mar 2001
Posts: 27
S
Stu T Offline
Member
Are we talking wiring devices, lugs or bussing ?

Re: Torque Frequency #3092 08/07/01 05:01 PM
Joined: Jan 2001
Posts: 29
S
sam Offline
Member
Does any of all use anti seize on your alum. connection? It seems to help get lug a little tighter in a panel box.

Re: Torque Frequency #3093 08/07/01 07:36 PM
Joined: Dec 2000
Posts: 4,283
electure Offline OP
Member
I was wondering only how often you might suggest to your customers that they be checked?
Yes, I NoAlox it all. In the thread of the lugs stops the sqweeeeek [Linked Image]
Tom's right-never without reterminating the connection


[This message has been edited by electure (edited 08-07-2001).]

Re: Torque Frequency #3094 08/07/01 08:16 PM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
Stu;
i think we're talkin' bigger stuff here, yet the same principals could apply to smaller.

i read some instructions, can't recall which, that asked no-lox be used as part of the listing ( it was refered to as something compound..)

today i busted off a meter lug, so a torque wrench is looking like a good idea. i was waaaaay out in the pukerbrush too, had to go 20+ miles to find the part.

as to the retorqueing;
what do other trades do, say mechanics. are different situations viewed differently? gasket vs. non-gasket? etc.... [Linked Image]

Re: Torque Frequency #3095 08/07/01 10:09 PM
A
Anonymous
Unregistered
Steel can mostly be retorqued as much as you wish provided that the parts are cool to the touch at the time.

When a gasket is involved, the procedure is usually to torque once and leave it. Torquing may actually be a long process requiring that the bolts be tightened incrementally in a certain sequence. Some engines may recommend retorquing after the first 20 hours of operation. There are engines with no head gasket too... I suppose they could be retorqued any time they were cool... but again this should not be necessary.

I see torquing a conductor more as a matter of how big a dimple does it need. Once it has that dimple, it has deformed and the pressure will be somewhat relieved over time as the conductor is squished out. Retorquing it will cause the dimple to enlarge. The difference here is that copper and aluminum are much softer than steel.

Re: Torque Frequency #3096 08/08/01 04:57 AM
Joined: Oct 2000
Posts: 5,389
S
sparky Offline
Member
agreed.
I was just wondering if other trades share our concerns here
[Linked Image]
After all, there are aluminum heads for cars.
Myself, i spent a decade putting together 6061 AL parts to specs of 1/10,000. The variables included all enviromental, as well as those introduced . The engineering aspects did not include any one-liner fits all explanations.
One item i do use is scotchcoat, which seems to isolate a termination well.

[This message has been edited by sparky (edited 08-08-2001).]

Re: Torque Frequency #3097 08/08/01 04:22 PM
Joined: Oct 2000
Posts: 3,961
Bill Addiss Offline
Member
Sparky,

In your thread awhile back you were searching for a word instead of Noalox .. It had probably said "anti-oxidant compound"

Bill


Bill
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sbi
sbi
indiana
Posts: 47
Joined: March 2008
Show All Member Profiles 
Top Posters(30 Days)
Popular Topics(Views)
271,004 Are you busy
205,006 Re: Forum
193,124 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3