Heat System Wiring #30878 10/31/03 07:15 AM
Joined: Mar 2003
Posts: 10
N
NorthernLights Offline OP
Member
I am wiring a radiant heat system in a new home. There are 14 Taco 007's on the system. They have a nameplate rating of .71A. Do you guys feel that this can run on a single 15A circuit? I don't think it will ever be a problem, due to the fact that not all pumps will be on at the same time, but will the inspector raise issue as to the number of motors on the circuit? Thanks

Work Gear for Electricians and the Trades
Re: Heat System Wiring #30879 10/31/03 09:24 AM
Joined: Oct 2003
Posts: 289
:
:andy: Offline
Member
i dont know anything about the NEC, but i personally would wire half of them to one breaker and half of them to a second breaker on the other phase, so the heating will still partially work if one phase is lost.

It just made me think as we had a phase lost in our street last week, and this was the phase our central heating was running on...

[This message has been edited by :andy: (edited 10-31-2003).]

Re: Heat System Wiring #30880 10/31/03 07:10 PM
Joined: Aug 2003
Posts: 173
S
Speedy Petey Offline
Member
Then which phase does he wire the boiler circuit to?

IMO if this is gas heat just run one circuit. It's only 10 amps combined so the inspector cannot say anything about the load being too much for a 15a circuit.
If it is oil fired you'll probably need another to carry the load of the boiler burner motor.


Speedy Petey

"Anyone who has never made a mistake has never tried anything new." -Albert Einstein

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
sparky66wv
sparky66wv
West Virginia
Posts: 2,236
Joined: November 2000
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 20
Popular Topics(Views)
272,256 Are you busy
206,143 Re: Forum
194,135 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3