#270 01/05/01 05:51 PM
Joined: Jan 2001
Posts: 18
A
Member
Can anyone tell me what the inrush current of a 480/208 75kva transformer would be if it was typically loaded on the secondary side at around 135 amps? I know it goes way high, but I need a ball park figure for argument sake. My boss wants to know why they keep popping the breaker when the transfer switch goes back to normal power. I need a ball park figure

#271 01/06/01 10:09 PM
Joined: Nov 2000
Posts: 72
B
Member
Alan: I calculated the maximum inrush current for a 75 KVA transformer as 990 amps.
I do not know the duration. The secondary load is irrelevant for inrush calculations.
A circuit breaker with a time trip curve that will permit 990 amps, with a duration necessary to establish core flux, would be required for starting the transformer.


Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC Now Available!
 
* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
TOOL_5150
TOOL_5150
Bay Area
Posts: 61
Joined: August 2007
Top Posters(30 Days)
BigB 9
triple 3
Popular Topics(Views)
302,376 Are you busy
231,776 Re: Forum
216,401 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5