ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 390 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#270 01/05/01 06:51 PM
Joined: Jan 2001
Posts: 18
A
Member
Can anyone tell me what the inrush current of a 480/208 75kva transformer would be if it was typically loaded on the secondary side at around 135 amps? I know it goes way high, but I need a ball park figure for argument sake. My boss wants to know why they keep popping the breaker when the transfer switch goes back to normal power. I need a ball park figure

#271 01/06/01 11:09 PM
Joined: Nov 2000
Posts: 72
B
Member
Alan: I calculated the maximum inrush current for a 75 KVA transformer as 990 amps.
I do not know the duration. The secondary load is irrelevant for inrush calculations.
A circuit breaker with a time trip curve that will permit 990 amps, with a duration necessary to establish core flux, would be required for starting the transformer.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5