Transformer inrush current #270 01/05/01 06:51 PM
Joined: Jan 2001
Posts: 18
A
Alan McNeil Offline OP
Member
Can anyone tell me what the inrush current of a 480/208 75kva transformer would be if it was typically loaded on the secondary side at around 135 amps? I know it goes way high, but I need a ball park figure for argument sake. My boss wants to know why they keep popping the breaker when the transfer switch goes back to normal power. I need a ball park figure

Work Gear for Electricians and the Trades
Re: Transformer inrush current #271 01/06/01 11:09 PM
Joined: Nov 2000
Posts: 72
B
Bennie R. Palmer Offline
Member
Alan: I calculated the maximum inrush current for a 75 KVA transformer as 990 amps.
I do not know the duration. The secondary load is irrelevant for inrush calculations.
A circuit breaker with a time trip curve that will permit 990 amps, with a duration necessary to establish core flux, would be required for starting the transformer.


Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
lil suzi
lil suzi
Midwest
Posts: 57
Joined: August 2003
Show All Member Profiles 
Top Posters(30 Days)
BigB 3
Popular Topics(Views)
270,731 Are you busy
204,964 Re: Forum
193,075 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3