Joined: Jul 2001
Posts: 2
OP
Junior Member
|
I need help on this one...........A large room as 4 rows of fluorescent fixtures. The contractor has jumped from row to row with Greenfield through the fixtures (not using any junction boxes). The fixtures are not listed as a raceway for circuit conductors. Is this legal?
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
welcome Marmat! I'm reading 410-31 and wondering exactly how the contractor 'daiseychained'. If done with 2 entries or 1 dual entry.
|
|
|
|
Joined: Jul 2001
Posts: 2
OP
Junior Member
|
Originally posted by sparky: welcome Marmat!
I'm reading 410-31 and wondering exactly how the contractor 'daiseychained'. If done with 2 entries or 1 dual entry.
The contractor fed the first row of fixtures with a 1/2" greenfield. He then came out of the same fixture to feed the next row (2 entries....one in-one out). This was then repeated for all the rows (in and out each fixture).
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Marmat; I mentioned the latter in hopes the wiring did not pass by the ballast, as it does , and it is not listed for such i'd say it is an inappropriate application.
|
|
|
|
Joined: May 2001
Posts: 176
Member
|
In your first post, you mentioned the fixtures are not listed for use as raceways. Art. 410-31 says specifically that fixtures shall not be used as a raceway for conductors. Exception No. 1 is for fixtures listed for use as a raceway. In several places in Art. 410, there is mention of an outlet box. I remember in the past that we were to design with outlet boxes, however I can't seem to find the requirement in the Code now. Although, check 410-67(c). Several commentary illustrations show an outlet box within one foot of the fixture, therefore, I think an outlet box adjacent to the fixture is the way to go.
|
|
|
|
Joined: Feb 2001
Posts: 54
Member
|
Been awhile since I looked for this one, but, as I remember....<G>, the fixtures Must have written on them suitable fer use as a raceway, and they must be installed end to end........
|
|
|
Posts: 3,682
Joined: October 2000
|
|
|
|
|