ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 265 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#24743 04/22/03 01:43 PM
Joined: Apr 2002
Posts: 178
R
Member
Can anyone help me find approx. dollar savings in the following situation.We have a bbc motor wired delta 220v 3ph pulling 60 amps.We rewired the motor Y 380 3ph and the load amps droped to 28amps.Before the motor was running on an older drive. Now we changed to a toshiba h3 transitor inverter.The motor is a 37kw.This came up in conversation but I`m not sure how to calculate the savings if there is any.Thanks in advance for any assistance you may have.

#24744 04/22/03 05:43 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Real Break:
Watts (KWHr) are the same, irregardless of voltage and amperage.
THere may be a savings if the demand (KW) is reduced by the new drive.
There are also some savings if you have a new high efficiency type motor. The basic calc for watts (KW) times time, will give you the base answer. As to the efficiency, the code letters, and the nameplate info should give you the data for that.

John


John
#24745 04/24/03 07:02 AM
Joined: Apr 2003
Posts: 48
M
Member
Dollars Savings Per Year =
0.746 x HP x [(1/EffA) - (1/EffB)] x hours x $/KWh

Where:

HP = load on the motor
EffA = efficiency of motor A at HP (expressed as decimal)
EffB = efficiency of motor B at HP (expressed as decimal)
EffA < EffB
Hours = hours of operation under load
$/KWh = average cost of electricity per kilowatt hour

The one large dynamic you have done is changed your power factor by raising the voltage . In doing this you have directly effected your motor efficiencys hence the savings.

Mike

#24746 04/24/03 04:41 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
There are {however “rosy”} examples at energy.copper.org, but the savings for one motor is probably not worth running the calculations. Losses in the drive probably offset any conductor savings. One somewhat related discussion is http://www.lmphotonics.com/energy.htm