GFI Connections #2446
07/10/01 06:17 PM
07/10/01 06:17 PM
C
chrispatti  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Deltona,Fla. United States
Can someone please tell me the correct way to hook 2 GFI's and 1 regular 20amp duplex receptacle using one circuit in a commercial building. The regular duplex receptacle cannot be on the load side of the GFI's. The 2 GFI's are for the men and ladies restroom and the regular duplex receptacle is for an office. I always thought you needed a seperate neutral for each GFI you put in line on one circuit.

Work Gear for Electricians and the Trades
Re: GFI Connections #2447
07/10/01 06:23 PM
07/10/01 06:23 PM
A
Anonymous
Unregistered

>Can someone please tell me the correct way to hook 2 GFIs and 1 regular 20amp duplex receptacle using one circuit in a commercial building. The regular duplex receptacle cannot be on the load side of the GFIs.
So just pigtail them off your branch (parallel).

>I always thought you needed a separate neutral for each GFI you put in line on one circuit.
No such requirement technically or in Code.

Re: GFI Connections #2448
07/10/01 06:29 PM
07/10/01 06:29 PM
C
chrispatti  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Deltona,Fla. United States
So you are saying to just go to the line side of the GFI's when making my connections,then I do not need another neutral? Will the GFI's ever trip if they sense an imbalanced load in whatever is plugged into the regular receptacle?

Re: GFI Connections #2449
07/10/01 06:45 PM
07/10/01 06:45 PM
R
Redsy  Offline
Member
Joined: Mar 2001
Posts: 2,056
Bucks County PA
Is this a multi-wire(2 or 3 hots and one neutral)circuit?

Re: GFI Connections #2450
07/10/01 06:55 PM
07/10/01 06:55 PM
C
chrispatti  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Deltona,Fla. United States
This is a single circuit application, 1 hot 1 neutral and a ground for 2 20amp GFI's and 1 20amp duplex receptacle.

Re: GFI Connections #2451
07/10/01 08:45 PM
07/10/01 08:45 PM
A
Anonymous
Unregistered

>So you are saying to just go to the line side of the GFIs when making my connections, then I do not need another neutral?
Correct.

>Will the GFIs ever trip if they sense an imbalanced load in whatever is plugged into the regular receptacle?[/B]
Not really. GFCIs are pretty clueless about the line side.
That's why they don't work if wired in backward (line and load interchanged).

Re: GFI Connections #2452
07/10/01 08:53 PM
07/10/01 08:53 PM
C
chrispatti  Offline OP
Junior Member
Joined: Jul 2001
Posts: 6
Deltona,Fla. United States
Thank You for your help. So the only time you would need a seperate neutral for each GFI is if they are all feeding from seperate circuits?

Re: GFI Connections #2453
07/10/01 09:53 PM
07/10/01 09:53 PM
A
Anonymous
Unregistered

>the only time you would need a separate neutral for each GFI is if they are all feeding from separate circuits?
That is correct. But that is because separate circuits need their own (line-side) neutrals by Code. This is not a technical requirement for a GFCI to operate.

However, the load side current must not be diverted anywhere. In other words, if you cross your load-side neutral with any other neutral, the GFCI will trip. And if any load on the GFCI is not hooked to the load-side neutral of that same GFCI, then when that load is activated, the GFCI will trip.



[This message has been edited by Dspark (edited 07-10-2001).]

Re: GFI Connections #2454
07/11/01 07:56 AM
07/11/01 07:56 AM
W
WARREN1  Offline
Member
Joined: May 2001
Posts: 176
Greenville, SC, USA
There was a time when GFCI's first came into the market, and were required by the NEC, that separate neutrals were required to prevent nuisance tripping.


Featured:

2017 Master Electrician Exam Preparation Combos
2017 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Grover
Grover
Sebago, ME, USA
Posts: 109
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 4
Popular Topics(Views)
252,835 Are you busy
189,626 Re: Forum
179,292 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.6.1
(Release build 20180101)
Page Time: 0.022s Queries: 14 (0.004s) Memory: 0.9950 MB (Peak: 1.1615 MB) Zlib enabled. Server Time: 2019-01-23 22:43:27 UTC