Good question — restaurant remodels are bread and butter for us, and the same things get missed over and over:
1. Nameplate loads, not rules of thumb. Every piece of cooking and refrigeration equipment needs a dedicated circuit sized off the actual nameplate. The classic failure is a multiwire circuit or a shared 20A that was "fine" until the second fryer showed up. Get the equipment schedule from the owner before you pull a single wire.
2. GFCI protection in the kitchen. 210.8(B) requires it on receptacles in kitchens/food prep areas, and inspectors fail restaurants on this constantly. Plan it from the start — GFCI breakers at the panel are cleaner than a pile of GFCI receptacles behind equipment nobody can reach to reset.
3. Spare capacity. Remodels always grow — another reach-in, a new POS station, outdoor seating heaters. I leave 20% spare breaker spaces and run a couple of spare conduits while the walls are open. Cheapest insurance you'll ever buy.
4. Hood and fire suppression interlocks. The Ansul system has to kill the cooking equipment and the makeup air has to be coordinated — that wiring gets forgotten until the fire marshal shows up.
5. Separate the POS/network gear from kitchen loads. A dedicated clean circuit for the register and network keeps you from chasing "mystery" reboots every Friday night.
The short version: get the equipment list first, then do the electrical plan around it — not the other way round.