1 members (Scott35), 335 guests, and 13 robots.
F
frank Offline OP
Health ans safety at my place of work wants gfci receptacles installed near the sinks in the break rooms. This is a contentious issue with inspection specifically where split receptacles are involved. We would have to then add circuits to meet new code as they do not make split gfci recpts . With no less then 25 break rooms inspection would want all break rooms brought up to new code which is not possible as most of the panels are full. As i rarely work in residential applications is it legal to just replace non split duplex receptacles with gfci or will the entire break room still need to be brought up to new code? The rational with inspection is that these break rooms currently meet code in regards to date of installation as such gfci receptacles are not required. Thanks in advance
The GFCI requirements might actually make Canada break with it's love of the split receptacle. I suppose the best solution would be GFCI breakers and separate circuits to the box. In the US we can get NM with 4 wires, 2 neutrals but it is not that common. I liked the concept at my house but I went with a 4" box and 2 receptacles in each counter top location, one duples on each circuit, then a regular GFCI receptacle works. (use a deep box)
Frank:
I passed on commenting on your post as I am not familiar with the Canadian EC but, here in New Jersey you can replace a regular duplex receptacle with a GFI receptacle, with no issue and no permit required.
That said, IF you have two (2) circuits with a common neutral (3 wire feed) could you convert the existing single gang box to a two gang?
IF so, why not pigtail the neutral, and install two GFI receptacles?
