#222128 03/08/23 09:05 AM
Joined: Apr 2002
Posts: 200
T
triple Offline OP
Member
My contention is that a steam humidifier (Carel model UE015XWOU1) can be considered a continuous load. This model is listed at 11.25 kw, 31.2 amps, 208 volts, three phase. 125% of 31.26 amps (figured from kw rating) is 39 amps. The inspector is allowing this load to be carried by an existing set of 10 thhn wires (35 amps in the 75 degree column). This is even neglecting the overfilled-with-16-C.C.C. pipe (50% derating) that these wires arrive in from the panel. Any comments?

Horizontal Ad
triple #222129 03/08/23 09:49 AM
Joined: Apr 2002
Posts: 200
T
triple Offline OP
Member
BTW, I neglected to add: 50% of 40 amps (90 degree column) results in only 20 amps

triple #222131 03/08/23 01:11 PM
Joined: Apr 2002
Posts: 7,407
Likes: 7
Member
My guess is '#10 at 35 amps, (didn't think continuous) nameplate says 31.2; OK'

May not have seen # of conductors in branch circuits conduit.

BTW, what is/was the outcome??


John

Link Copied to Clipboard
Advertisement:-Right


Tools for Electricians
Tools for Electricians
 

* * * * * * *
2023 National Electrical Code (NEC)
2023 NEC + Exam Prep Study Guides Now Available!
 

Member Spotlight
NickD
NickD
Amish Country, PA
Posts: 46
Joined: March 2013
Top Posters(30 Days)
Popular Topics(Views)
333,593 Are you busy
258,964 Re: Forum
240,393 Need opinion
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5