ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

>> Home   >> Electrical-Photos   >> Classifieds   >> Subscribe to Newsletter   >> Store  
 

Photos of the Week:

Avalon Theatre
Avalon Theatre-1 2 3 4

Random Gallery Image:
Recent Gallery Topics:
What in Tarnation?
What in Tarnation?
by timmp, September 10
Plumber meets Electrician
Plumber meets Electrician
by timmp, September 10
Who's Online Now
0 members (), 135 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#222085 01/10/23 06:08 PM
Joined: Aug 2022
Posts: 3
G
New Member
Found this and was looking for some feedback: 400 amp fused switch that has parallel feeders that terminate under one lug. Checked nameplate on panel, see that 2 wires per lug seems to be shown in the table.

Is this allowed even if nameplate seems to allow it?

Also some other panels with parallel feeds under single lug. Didn't see anything about 2 wires per terminal on the panelboard.

Thanks
GW

Attached Images
Facebook_creation_2338816.jpg Facebook_creation_1173200.jpg 20230109_130616.jpg
Horizontal Ad
Joined: Jul 2004
Posts: 10,007
Likes: 37
G
Member
That is what I call hold your nose legal. You may not think it passes the smell test but if the manufacturer had it listed for 2 wires and the instructions say it is OK for 2 wires, it is OK. The only caveat is deep in the fine print it may say "2 of the same size wires". If you stick a #14 in a lug with a #2 there is a real good chance that #14 will not have a decent connection.


Greg Fretwell
Joined: Apr 2002
Posts: 7,412
Likes: 8
Member
It may be a 'hold your nose' thing, but when I had tools, I would not do it. (Period)

I have not seen anyone do this.

As an inspector, based on what the label stated, I have to take it. However, I would call Siemens and question that label.


John

Link Copied to Clipboard
New Page 2
Powered by UBB.threads™ PHP Forum Software 7.7.5