#222085 01/10/23 06:08 PM
Joined: Aug 2022
Posts: 3
G
New Member
Found this and was looking for some feedback: 400 amp fused switch that has parallel feeders that terminate under one lug. Checked nameplate on panel, see that 2 wires per lug seems to be shown in the table.

Is this allowed even if nameplate seems to allow it?

Also some other panels with parallel feeds under single lug. Didn't see anything about 2 wires per terminal on the panelboard.

Thanks
GW

Attached Images
Facebook_creation_2338816.jpg Facebook_creation_1173200.jpg 20230109_130616.jpg
Tools for Electricians:

Tools for Electricians, Installers & Maintenance Technicians

Joined: Jul 2004
Posts: 10,041
Likes: 37
G
Member
That is what I call hold your nose legal. You may not think it passes the smell test but if the manufacturer had it listed for 2 wires and the instructions say it is OK for 2 wires, it is OK. The only caveat is deep in the fine print it may say "2 of the same size wires". If you stick a #14 in a lug with a #2 there is a real good chance that #14 will not have a decent connection.


Greg Fretwell
Joined: Apr 2002
Posts: 7,413
Likes: 9
Member
It may be a 'hold your nose' thing, but when I had tools, I would not do it. (Period)

I have not seen anyone do this.

As an inspector, based on what the label stated, I have to take it. However, I would call Siemens and question that label.