191
26
Posts: 7,381 Likes: 7
I have seen a few with copper water pipe of the 1/2" and 3/4", on rooftop HVAC units. Usually with a few blown fuses laying around. Have not come upon any pipe nipples yet.
The disconnect in this pic would get a red sticker, unsafe, be shut down at the source of the feeder.
Posts: 4,116 Likes: 4
Very Dangerous!
Posts: 9,928 Likes: 34
I am hoping that is just being used as a disconnect and there is OCP somewhere up stream. If so it is just a 110.3(B) but still worth a violation. They do make "Breakers" with about the same over current protection and they are legal (no numbers on the handle). It is just a switch that fits in a breaker slot. I always thought that was dangerous in the hands of the untrained.
OK, looking at the pic again, I would def red tag this and do an unsafe notice.
The disconnect is damaged besides the fuse issue. "A" phase will not open! Look carefully as the insulating mechanism that pulls out the cutout is damaged. The spring that tightens the cutout receiver is damaged. "C" phase also looks like it also has issues, but I cannot enlarge the pic enough.
The conductors appear to have heat issues from the pic. An accident waiting to happen.
Posts: 943 Likes: 2
The problem with all poles not being opened when shutting off the switch was not as prevalent in that generation of Cutler-Hammer safety switches, but was quite common in the version it replaced, the insulator would just break, not fail from overheating like the example above.
