Hello all,

I am a new forum member and have a question pertaining to something different I ran across on the Electrical section of the current set of prints I am reviewing.

This is a remodel and from everything I can tell, most everything is fairly straight forward.. However, I ran into a Diagram Note that reads:

"Existing building service to remain and be reused. Contractor to verify distribution and protection to existing panel "K10" and provide new 220A feed and Overcurrent protection if not existing. Coordinate any work required with existing conditions and building engineer."

Most of the note is understood, ... Existing Panel K10 remains but needs tested since the circuits will be completely changed.. The only place I have a question is the "provide new 220A feed and Overcurrent protection if not existing" sentance.. I understand this to mean that a new 220 feed needs to be provided and then only add the Overcurrent protection if it doesn't already exist..

I really hope I am not making way too much out of this note.. Am I correct in my assumption? Or am I way off?

Thank you for all your help!!

Joined: Jul 2004
Posts: 9,663
Likes: 4
G
Member
I read that to say they are modifying K10 (panel) and the load may change. Verify that the feeder ampacity and O/C protection is adequate and replace it if it is not. It might also mean that if the feeder is a tap they want O/C protection at the source end. If this is not clear you could always kick it back for a better explanation or description of the scope of work. It is better to have this clear now than later in the project. It may also alter the contractors bid so I assume they would like to know now too.


Greg Fretwell

Link Copied to Clipboard
Featured:

Tools for Electricians
Tools for Electricians
 

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
Theelectrikid
Theelectrikid
Levittown, PA
Posts: 811
Joined: April 2004
Top Posters(30 Days)
timmp 3
rick99 1
Popular Topics(Views)
283,573 Are you busy
216,870 Re: Forum
203,218 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.5