You will never guess #220829 06/05/20 05:45 PM
Joined: Mar 2004
Posts: 782
B
BigB Offline OP
Member
why the AFCI kept tripping. New house, finishing up a few odd items today when the floor cleaners came to me and said "soon as we try to use our vacuum in the front bedroom the breaker trips" Huh, must be your vacuum, nobody else has tripped a breaker yet, so I reset the breaker and try my shop vac, trips almost immediately. This circuit has been up and running for months with no issues, lights working fine, plugs work fine except for the vacs. I swapped the breaker with another, problem stays with the circuit. Went on to do some other things so I could ponder on it a while.

Next job, owner wants the bath wall sconce flipped over in the bath that goes with this bedroom, go in there to do that when I noticed a faint humming coming from the 110 CFM exhaust fan which is COMPLETELY COVERED WITH BLUE TAPE AND CAN'T GET ANY AIR. Apparently the tilers covered it to keep dust out, or maybe it was the painters. Once the tape was removed all was well. So the fan must have been really over-amping and the vacs were enough to throw the circuit over the edge, of course first thoughts are always a wiring error or bad AFCI now days.

Just goes to show, I have learned over the years when troubleshooting not to just rush in and tear everything apart right away. It usually pays to think about it for a while and reason things out.

Last edited by BigB; 06/05/20 05:46 PM.
Work Gear for Electricians and the Trades
Re: You will never guess [Re: BigB] #220831 06/06/20 10:52 AM
Joined: Mar 2004
Posts: 782
B
BigB Offline OP
Member
20 years ago we would have grabbed the amp clamp first thing, what I'm trying to say is the AFCIs have changed the way we think about troubleshooting, we are much more conditioned to believe we have a wiring error than an overload which can lead to wasted time.

Re: You will never guess [Re: BigB] #220832 06/06/20 04:38 PM
Joined: Jul 2004
Posts: 9,577
G
gfretwell Online Content
Member
It would be nice if all AFCIs came with diagnostics, an LED that comes on for arc faults and another for ground faults.


Greg Fretwell
Re: You will never guess [Re: BigB] #220837 06/12/20 03:20 AM
Joined: Jul 2002
Posts: 8,390
Trumpy Offline
Member
BigB,
That's quite interesting, I would have suspected something like bad brushes/ commutator in the vacuum cleaner motor.

Re: You will never guess [Re: BigB] #220889 07/13/20 04:08 AM
Joined: Aug 2008
Posts: 60
A
andey Offline
Member
That sounds very foul to me.
I looked up the first 110 CFM bathroom fan datasheed i could find and it has 0.2 amps nominal current. This would only increase a little bit covered up, if not decrease (depending on the fan design).
Where should it dispass all the heat. otherwise, it would bake the windings and hopefully trip the thermal protection.
I'm very sure there is another fault hidden somehwere in the house that tripped the AFCI.

Re: You will never guess [Re: andey] #220890 07/13/20 09:45 AM
Joined: Mar 2004
Posts: 782
B
BigB Offline OP
Member
Originally Posted by andey
That sounds very foul to me.
I looked up the first 110 CFM bathroom fan datasheed i could find and it has 0.2 amps nominal current. This would only increase a little bit covered up, if not decrease (depending on the fan design).
Where should it dispass all the heat. otherwise, it would bake the windings and hopefully trip the thermal protection.
I'm very sure there is another fault hidden somehwere in the house that tripped the AFCI.


All I can tell you is that as soon as I uncovered the fan everything went back to normal and the owners have been in there for a month now with no issues. Maybe it wasn't an overload but some other motor related phenomena that caused it it simulate an arc fault.

Re: You will never guess [Re: BigB] #221188 02/15/21 06:24 PM
Joined: Feb 2010
Posts: 6
S
SMOKEYBOB Offline
New Member
Trouble shooting tip:ALWAYS LOOK AT THE SIMPLE THINGS 1ST!!!
A shorted CFL almost cost me a reinspection fee

Re: You will never guess [Re: BigB] #221190 02/22/21 01:57 PM
Joined: Oct 2000
Posts: 3,974
Bill Addiss Offline
Member
Had a service call once where the Bathroom Heater/Fan was tripping the GFCI Breaker.

After taking everything apart and reassembling twice and swapping out Breaker I found out there was a direct short in the Heat Bulb.


Bill
Re: You will never guess [Re: BigB] #221193 02/22/21 02:34 PM
Joined: Apr 2002
Posts: 7,238
HotLine1 Offline
Member
Craziest service call I had was 'No lights in stockroom' at about 7PM for a national sport apparel/shoe store.

Checked the panel, employee said lights are on controller; that checked out OK. Started following conduit, saw box by entry to stockroom wall, hmmmmm......

Moved a few sneaker boxes............low and behold a toggle switch in 'off' position. Flipped it 'on'! Manager was in shock! Apparently, a box hit the switch that no one knew was there???

To save face, I removed the switch and spliced thru, as the controller was operational.


John
Re: You will never guess [Re: BigB] #221197 02/24/21 05:45 PM
Joined: Oct 2000
Posts: 3,974
Bill Addiss Offline
Member
It's surprising how many times I solved a non-working outlet problem by turning on a switch that the Homeowner said didn't do anything.


Bill
Page 1 of 2 1 2

Featured:

2020 National Electrical Code
2020 National Electrical
Code (NEC)

* * * * * * *

2020 Master Electrician Exam Preparation Combos
2020 NEC Electrician
Exam Prep Combos:
Master / Journeyman

 

Member Spotlight
renosteinke
renosteinke
Blue Collar Country
Posts: 5,316
Joined: January 2005
Show All Member Profiles 
Top Posters(30 Days)
Trumpy 11
Popular Topics(Views)
277,895 Are you busy
211,384 Re: Forum
198,428 Need opinion
Powered by UBB.threads™ PHP Forum Software 7.7.3